    Exclamation Phase Rotation/Compressor Sensitivity



    Hey guys, wondering if I could get some advice about a situation I have at the moment....I have a tecumseh 3 Phase recipricating Compressor Model Tagp2516z which was a replacement for a Copeland Scroll Model ZF13K-TSV-556. I changed from the Copeland to the Tecumseh as the Copeland had been running inefficiently. Upon connection of the Tecumseh Compressor I noticed the Phase Rotation was incorrect(for the Copeland Scroll). I performed acid tests for the oil, no acid was present, tripple vacced the system and charged with R404A. The compressor ran fine until it reached -17 degrees then struggled to hold that temperature. Suction pressure was -35 degrees C, ambient teperatures were 38 degrees C, and condensing pressure was at 52 degees C. The coldroom ran for 1 week and the new compressor has now failed resistence betwwen L1 and L3 and has failed to earth.

    Upon further inspection, a newly commissioned 3 Phase generator was auto swiching on mains power failure and was noticed to be switching phases(L2, L3 - opposite to incoming power supply) with a delay time of no more than 30 seconds.

    Has this caused my compressor failure??? Please help as this is URGENT!!!



  2. #2
    Join Date
    Dec 2005
    Location
    SCOTLAND
    Age
    51
    Posts
    47
    Rep Power
    0

    Re: Phase Rotation/Compressor Sensitivity

    Not sure if i can help but running a generator instead of mains power can often cause problems with compressors on start up...is it possible to isolate the generator from your kit until you replace comp and have it running on trial?

  3. #3
    Join Date
    Sep 2008
    Location
    england
    Posts
    429
    Rep Power
    20

    Re: Phase Rotation/Compressor Sensitivity

    Just and idea here. If the genny had kicked in automatically on power failure maybe the high and low pressures in the compressor hadn`t had time to equalise (or any where near equalisation) thus causing it to overload. Was the overload matched to the new comp?
    I seem to remember that scroll comps are more tolerant of reverse running but I wouldn`t like to put a tenner on it.
    If there is a danger of this happening again with a power outage maybe fitting an auto restart with a timer to allow equalisation would be an idea.

    Regards,
    Glenn

  4. #4
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Phase Rotation/Compressor Sensitivity

    Was the direction of rotation of the oil pump correct ? Oil pressure diff relay set correct ?

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Phase Rotation/Compressor Sensitivity

    Tagp2516z is a small hermetic compressor.

    There is no way you can tell the rotation direction. Only after start up. There is no arrow to indicate the rotation.

    Therefore the sequence of the phases has absolutely no importance.

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Phase Rotation/Compressor Sensitivity

    Infact no matter what is the rotation, hermetic and semihermetic compressors can operate in both directions. Scrolls are different story altogether.
    But, the genset surely spikes when kicks in, and a high voltage transient can pierce the insulation laquer.

  7. #7
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Phase Rotation/Compressor Sensitivity

    Hi,

    I’ve heard of previous scroll compressor failure due to back up generators being wired with a different phase sequence (but never a recip compressor). Units with scroll compressors have reverse phase protection devices, however the reaction time of the protection device wasn’t quick enough to detect the change in phase sequence. The generators will kick in fairly quick and most devices only check phase sequence when power is applied but will detect a phase failure.

    This raises an interesting question,
    How would a reciprocating compressor react to a phase sequence change during operation?
    Obviously if the compressor stopped it would then be attempting to start against high pressure (no time to equalise).

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Phase Rotation/Compressor Sensitivity

    When rotation direction is critical, a phase sequence relay must be installed to protect the compressor.

  9. #9
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Phase Rotation/Compressor Sensitivity

    This raises an interesting question,
    How would a reciprocating compressor react to a phase sequence change during operation?
    It Will break into small pieces......

  10. #10
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Phase Rotation/Compressor Sensitivity

    Quote Originally Posted by chemi-cool View Post
    When rotation direction is critical, a phase sequence relay must be installed to protect the compressor.
    I agree, but as I said most reverse phase protection devices will not detect a change in phase sequence during operation.
    Example: back up generator kicking in during operation, power on/off/on is quicker than reaction time of protection device.
    Last edited by VRVIII; 31-01-2010 at 06:15 PM.

  11. #11
    Join Date
    Sep 2008
    Location
    england
    Posts
    429
    Rep Power
    20

    Re: Phase Rotation/Compressor Sensitivity

    Quote Originally Posted by VRVIII View Post
    Hi,


    This raises an interesting question,
    How would a reciprocating compressor react to a phase sequence change during operation?
    Obviously if the compressor stopped it would then be attempting to start against high pressure (no time to equalise).
    Well, on a large recip you could have the problems with trying to reverse a large rotating mass ie massive strain on a coupling or shredded belts.
    On a small recip I`d have though an overload relay should protect the motor
    This why I`d suggest a auto restart facillity if power outage could cause problems on a critical system.

  12. #12
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Phase Rotation/Compressor Sensitivity

    Quote Originally Posted by glenn1340 View Post
    Well, on a large recip you could have the problems with trying to reverse a large rotating mass ie massive strain on a coupling or shredded belts.
    On a small recip I`d have though an overload relay should protect the motor
    This why I`d suggest a auto restart facillity if power outage could cause problems on a critical system.
    Cheers Glen, I totally agree
    BTW if a scroll compressor is operated in reverse it will rapidly overheat and kill compressor

  13. #13
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Phase Rotation/Compressor Sensitivity

    when you replaced the compressor,did you replace contactor and o/load, what reason for initial compessor failure mechanical/electrical,seen many second failures due to contactors so i always change em also seen a lot of guys change single phase hermetics and never fit the new electrics that are supplied with em?

  14. #14
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Phase Rotation/Compressor Sensitivity

    A lot of hermetic compressor run around 2900rpm, i wonder how quickly the changeover is and if its gone from clockwise to anti clockwise a few times and snapped something, nearly a 6000rpm difference!
    I wonder as the scroll has an orbiting motion if it would have as much inertia, also the tend to want to spin backwards when they stop so this would help in a way.

  15. #15
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Phase Rotation/Compressor Sensitivity

    There must be a simple way to protect the electrical system and the other components from turning back wards when a generator comes in.

    I am seeing tomorrow a person from the national electric company for connecting a 5 MW solar system and I will ask him about that protection.

  16. #16
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Phase Rotation/Compressor Sensitivity

    Quote Originally Posted by chemi-cool View Post
    There must be a simple way to protect the electrical system and the other components from turning back wards when a generator comes in.

    I am seeing tomorrow a person from the national electric company for connecting a 5 MW solar system and I will ask him about that protection.
    The generator out put should be tested and ensure this has the same phase sequence as mains supply.

  17. #17
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Phase Rotation/Compressor Sensitivity

    It shouldn't kick in at once. Generally, a bank of batteries connected to a three phase UPS should provide seconds to minutes of back up, while generator settles.

  18. #18
    Join Date
    Oct 2005
    Location
    In a 2 bedroom unit. Why's That? :)
    Posts
    314
    Rep Power
    19

    Re: Phase Rotation/Compressor Sensitivity

    Quote Originally Posted by chemi-cool View Post
    Tagp2516z is a small hermetic compressor.

    There is no way you can tell the rotation direction. Only after start up. There is no arrow to indicate the rotation.

    Therefore the sequence of the phases has absolutely no importance.
    Hi mate. I have a rotation analyzer and it does have a little arrow . It's placed across the incoming phases to indicate clockwise or anti clockwise direction.

    ...But the real issue I face is, if the compressor stops, for 30secs to 1 min, then starts with reverse rotation, then instantaneously reverses back to correct rotation whilst still running, when the genset drops out, will this have a dramatic effect as I've seen in this instance?????

    BTW there is no battery bank on the genset.

  19. #19
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Phase Rotation/Compressor Sensitivity

    its poor windings,apart from that my opinion is that they should work in a bucket of water
    mmm to beer or not to beer...........lets drink breakfast

  20. #20
    Join Date
    Oct 2005
    Location
    In a 2 bedroom unit. Why's That? :)
    Posts
    314
    Rep Power
    19

    Re: Phase Rotation/Compressor Sensitivity

    ...... More info........... When the motor grounded, most of the oil blew out of the compressor back up the suction line. the contamination has been localized to the compressor sump, suction line and accumulator. No acid.

  21. #21
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Phase Rotation/Compressor Sensitivity

    We had a long discussion about that issue.

    What they do is very simple,
    After the main switch, [Isolator in UK] there is a sequence relay that operating a control relay or a small contactor.
    If mains falls and generator kicks in, there is momentary cut out of the electricity, when it comes back from the generator, it goes through the same control circuit and it takes for that sequence relay Ms to check the phase sequence. If all OK, it will start the control circuit.

    And therefore there no way the compressor will change its rotation direction.

    I hope you all understand what I mean.

  22. #22
    Join Date
    Feb 2009
    Location
    india
    Posts
    17
    Rep Power
    0

    Re: Phase Rotation/Compressor Sensitivity

    you not mention there is timer or no?
    in three phase less chane compare to single phase

  23. #23
    Join Date
    Oct 2005
    Location
    In a 2 bedroom unit. Why's That? :)
    Posts
    314
    Rep Power
    19

    Re: Phase Rotation/Compressor Sensitivity

    Quote Originally Posted by chemi-cool View Post
    We had a long discussion about that issue.

    What they do is very simple,
    After the main switch, [Isolator in UK] there is a sequence relay that operating a control relay or a small contactor.
    If mains falls and generator kicks in, there is momentary cut out of the electricity, when it comes back from the generator, it goes through the same control circuit and it takes for that sequence relay Ms to check the phase sequence. If all OK, it will start the control circuit.

    And therefore there no way the compressor will change its rotation direction.

    I hope you all understand what I mean.
    I understand what you are saying chemi-cool, but the the situation remains that when the genset was commissioned, it wasn't commissioned correctly. We had a call out to a cold room at the same location as the phases had been reversed and therefore the compressor on that system was running loud and inefficient. once the generator power dropped out, the compressor began working again... this was a scroll type. After this was noticed the commissioning electrician returned to correct the phase issue with the genset.... 3 days later the reciprocating compressor grounded.

Similar Threads

  1. 3 phase 220v
    By CHIZEL010 in forum Trouble Shooting
    Replies: 16
    Last Post: 14-10-2009, 01:26 PM
  2. single phase 208v
    By j.a.violante in forum Air Conditioning
    Replies: 2
    Last Post: 24-05-2009, 07:18 AM
  3. generic single phase contactor?
    By paul_h in forum Electrical
    Replies: 9
    Last Post: 06-02-2009, 09:28 AM
  4. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Replies: 5
    Last Post: 04-01-2008, 06:11 PM
  5. 3 phase connections
    By davidler in forum Industrial
    Replies: 2
    Last Post: 22-03-2004, 03:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •