    Blended Refrigerants & Oil carryover



    Guys,

    In my short membership of this site i have noticed a significant amount of issues relating to Oil carryover..
    I just wanted to share my experiance with this issue in retrofitted & dedicated blended systems..
    At the time of phase out, i was doing a significant amount of trawler work All Bitzers (Bitzer crap purchased @ auctions & made to work somehow). There were 8 new gasses & 3 new oils coming out everyday.. Because of this chaos, we didn't retrofit anything until we had no option..
    We did however work on a significant number of migratory boats that had been retrofitted & weren't performing.
    High Discharge temps & pressures / High Oil carryover / Burned Oil.
    In the space of 1 month i looked at 3 systems with broken discharge valves .. All 3 had water cooled heads (small Head volume)
    This indicated that the expansion of blended refrigerants in the compression phase was far more severe than it was with *****s.
    From that point i upgraded every discharge valve, discharge line, oil seprator ( Equal size to Suction) right through to the condensor, ( approx 50 boats..)

    This by itself ..
    Eliminated Oil Carryover. Reduced Discharge pressure to the point that condensor flows required regulating to maintain pressure drop. Oil would come out looking clean. Refig performance 100% improvement, in most cases better than they ran on *****
    I'm not convinced that manufacturers are designing Blend friendly systems to this day..

    Hope this helps someone..



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Blended Refrigerants & Oil carryover

    Interesting post Mark.

    Cheers Jon

  3. #3
    Join Date
    Dec 2008
    Location
    USA
    Age
    42
    Posts
    57
    Rep Power
    16

    Re: Blended Refrigerants & Oil carryover

    So upgrading the line size helped slow down the velocity of the refrigerant which in turn allowed the system to not carry the oil to the parts of the system that shouldn't have oil?

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Blended Refrigerants & Oil carryover

    I don't get the whole posting. What do you mean by: "the expansion of blended refrigerants in the compression phase was far more severe than it was with *****s"?

    And what did you exactly upgrade? You mean you oversized?

  5. #5
    Join Date
    Oct 2009
    Location
    Australia
    Age
    52
    Posts
    24
    Rep Power
    0

    Re: Blended Refrigerants & Oil carryover

    Quote Originally Posted by NoNickName View Post
    I don't get the whole posting. What do you mean by: "the expansion of blended refrigerants in the compression phase was far more severe than it was with *****s"?

    And what did you exactly upgrade? You mean you oversized?
    Nick,

    I mean if it had a 3/4" discharge service valve, I;d fit a 7/8" & bring that up to a 1"1/8 oil sep, Most of the marine stuff here had Northside Condensers that had an 1"1/8 connection that had been reduced back down.. I'd run the whole line in 1"1/8..

    With ***** if you ran a nice low superheat you could run a nice steady oil temp..You could see oil in the oil return line not foam.. I have found with blends,,As soon as you get the superheat down to where it should be the compressors/ oil & discharge all heat up.. How many MOP valves were we fitting to ***** systems ??

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Blended Refrigerants & Oil carryover

    I can't follow you.
    First, pipe size should not be a guess or a trial and error game. There are gazillions of pages about how to size the three refrigeration lines properly. I'm not ready to take the advice about increasing pipe sizes just based on experience.

    Secondly I can't follow you on the oil to foam thing. Are you saying that blends are more prone to foaming? What refrigerants, what oil?

    Thirdly, why on earth a low superheat in a blended refrigerant causes high discharge temperature, while the opposite is the case with single-component refrigerants?

  7. #7
    Join Date
    Oct 2009
    Location
    Australia
    Age
    52
    Posts
    24
    Rep Power
    0

    Re: Blended Refrigerants & Oil carryover

    Quote Originally Posted by NoNickName View Post
    I can't follow you.
    First, pipe size should not be a guess or a trial and error game. There are gazillions of pages about how to size the three refrigeration lines properly. I'm not ready to take the advice about increasing pipe sizes just based on experience.

    Secondly I can't follow you on the oil to foam thing. Are you saying that blends are more prone to foaming? What refrigerants, what oil?

    Thirdly, why on earth a low superheat in a blended refrigerant causes high discharge temperature, while the opposite is the case with single-component refrigerants?
    Nick,

    FIRST: You don't have to take my advice.
    The discharge line is the shortest run in the system. On a condensing unit ,1?2? meters ? Trawler 3? 4 meters ?.. You're old enough to remember that retrofitting was a trial & error game..Key Note Speakers @ trade nights would tell us that: "A sight glass, is no longer a sight Glass You will never clear them.. T/X valves do run on flash gas after all"..
    Synthetic Oil was being sold in Plastic containers & spoiling on the shelf..& Every new Refrigerant on the market was better than every other refigerant on the market..

    Second: 507 EAL32.. 404 EAL32.. This may disturb you greatly Nick,, but i inherited a fleet off a Fridgie who moved up to Cooktown to replace the one who blew himself up pressure testing with Oxy..(30 years exp).
    All his boats were on 507 & 3GS.. Oil came out Clear everytime.. These things get a Hot Start every trip.. Tonnes of salt water pumped into the deckboxes as they steam out. They endure prolonged periods of high load.. If there is a high flow of foaming oil pissing though the return line the sump will get hotter & hotter..

    Third: If a retrofitted system is stuggling with Oil Carryover.. Lowering the superheat will not decrease the sump temp at all..

  8. #8
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Blended Refrigerants & Oil carryover

    Very interesting thread, indeed, Mark II.

    If you could perhaps take dimensions of a few examples you've mentioned - including compressor details, operating pressures, temps - we could have a look at what exactly is going on in the system both before (on R22) & after (blends). We can then check the line sizes properly, & all learn from your valuable experiences.

    An ounce of hands-on learning is worth 1000 tonnes of guestimating. Your practical experiences are extremely valuable.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  9. #9
    Join Date
    Oct 2009
    Location
    Australia
    Age
    52
    Posts
    24
    Rep Power
    0

    Re: Blended Refrigerants & Oil carryover

    Des,

    I stopped doing Trawlers about 8 years ago.. These days i'm based at an industrial chemicals complex / Explosives plant doing mainly Ammonia work..

    The basis of this thread is:There is higher veocity in the discharge phase of blended systems. Creating volume helps to slow it all down.. Allows oil to settle in the seperator & be retuned as oil without heating up the sump..

  10. #10
    Join Date
    Jan 2010
    Location
    atlanta
    Age
    33
    Posts
    14
    Rep Power
    0

    Re: Blended Refrigerants & Oil carryover

    ya the oil will mes **** up

  11. #11
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Blended Refrigerants & Oil carryover

    Quote Originally Posted by Mark II View Post
    Nick,
    "A sight glass, is no longer a sight Glass You will never clear them.. T/X valves do run on flash gas after all"..
    Synthetic Oil was being sold in Plastic containers & spoiling on the shelf..& Every new Refrigerant on the market was better than every other refigerant on the market..
    Now I follow you.

    Quote Originally Posted by Mark II View Post
    If there is a high flow of foaming oil pissing though the return line the sump will get hotter & hotter..
    507 and 3GS do not like each other. MO and HFC should not be together in a circuit.

    Quote Originally Posted by Mark II View Post
    Third: If a retrofitted system is stuggling with Oil Carryover.. Lowering the superheat will not decrease the sump temp at all..
    No, in fact increasing the superheat should decrease carry over and sump temperature.

Similar Threads

  1. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  2. Are there standard-systems for natural refrigerants?
    By Moeller in forum Refrigerants
    Replies: 9
    Last Post: 25-05-2009, 10:01 AM
  3. Blended refrigerants
    By yousufrafi in forum Refrigerants
    Replies: 4
    Last Post: 25-02-2009, 10:24 AM
  4. Refrigerants and The Environment
    By Josip in forum Refrigerants
    Replies: 18
    Last Post: 18-12-2008, 05:53 PM
  5. Hydrocarbon refrigerants
    By mbeychok in forum Refrigerants
    Replies: 15
    Last Post: 01-09-2006, 10:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •