    reds007's Avatar
    reds007 Guest
    Compressor Capacity Troubleshooting Help
    I'm designing new system with an LG Compressor...I finished charging it but the system capacity is about 20% below what it should be. The capacity on spec sheets at these temperatures should be 9400btuh.
    However I get 8000btuh. The amperages I am getting are also much less than the ones on the spec sheets.
    I'm thinking it might be a wrong compressor spec?
    Can someone please help me troubleshoot it?
    Here are the numbers I got:
    Refrigerant = R410A
    Evap Temp = 45degF
    Compressor Temp = 105degF
    TXV System
    Superheat = 8degF
    Subcooling = 15degF
    Let me know if you need any more info.
    Thanks,
    Reds
    11,025
    Re: Compressor Capacity Troubleshooting Help
    How are you measuring the loading on the system?
    Aug 2009
    New Zealand
    2,554
    Quote Originally Posted by reds007 View Post
    Refrigerant = R410A
    Evap Temp = 45degF
    TXV System
    Superheat = 8degF
    Subcooling = 15degF
    Thanks,
    Reds
    Are the compressor specs at these conditions, if not you can not compare. you change any one of the above, then the performance will change.
    As Brain says what is accuracy of your loading.
    reds007's Avatar
    reds007 Guest
    Thanks guys for the reply.
    The rated conditions are for Evap = 45degF, Condenser = 105degF, Superheat = 50degF, Subcooling = 15degF
    The capacity was obtained by measuring the water loop temperature difference.
    Capacity = 500 * GPM * (Water In - Water out)
    (Heat pump in heating mode)
    I did the same measurement on our older R22 units and the capacities of those units are very close to rated.
    Right now I'm thinking its the compressor. So after the weekend I will try to build another unit with a Tecumseh compressor.
    Would there be another reason for loosing capacity? I'm pretty sure the piping sizing is correct.
    I appreciate your help. Let me know if you need any other info.
    Reds
    Apr 2001
    79
    5,071
    35
    Did you measure GPM?... or use an estimate?
    Aug 2009
    New Zealand
    2,554
    Reds
    With lower current, and lower performance, indicates as noted, ratings are not for that compressor, or the compressor has the wrong label. (incorrect displacement)
    11,025
    Also, at moment we don't have any measured readings as yet from what I can see.
    In one post you stated the evaporator and condenser temperatures as measured and in the second you state that they are design.
    Have you got exactly the design operating conditions?
    Your subcooling seems as per spec but the superheat is way off.
    reds007's Avatar
    reds007 Guest
    The measured evaporator and condenser temperatures were +/- 3%
    Flow was measured with a turbine type flow meter.
    The only measurement that was off was the superheat. I will try to adjust it higher before I try changing compressors but I don't think it will increase performance much.
    Thanks.
  1. need troubleshooting charts
    By mcm12263 in forum New to RE
    Last Post: 13-05-2009, 10:19 PM
  2. troubleshooting books
    By marc5180 in forum Refrigeration Books
    Last Post: 04-04-2009, 06:08 PM
  3. Daikin VRV Troubleshooting
    By ral in forum Fundamentals
    Last Post: 30-09-2008, 08:36 PM
  4. Troubleshooting a vacuum pump and gauge set.
    By Old Codger in forum Fundamentals
    Last Post: 08-08-2008, 05:13 PM
  5. Looking For A Good Troubleshooting Guide
    By nightranger121 in forum Trouble Shooting
    Last Post: 23-11-2007, 06:16 PM