Compressor Capacity Troubleshooting Help
Hi,
I'm designing new system with an LG Compressor...I finished charging it but the system capacity is about 20% below what it should be. The capacity on spec sheets at these temperatures should be 9400btuh.
However I get 8000btuh. The amperages I am getting are also much less than the ones on the spec sheets.
I'm thinking it might be a wrong compressor spec?
Can someone please help me troubleshoot it?
Here are the numbers I got:
Refrigerant = R410A
Evap Temp = 45degF
Compressor Temp = 105degF
TXV System
Superheat = 8degF
Subcooling = 15degF
Let me know if you need any more info.
Thanks,
Reds
-
29-01-2010, 10:42 PM #2
Re: Compressor Capacity Troubleshooting Help
How are you measuring the loading on the system?
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
29-01-2010, 11:44 PM #3
-
30-01-2010, 06:44 PM #4
Re: Compressor Capacity Troubleshooting Help
Thanks guys for the reply.
The rated conditions are for Evap = 45degF, Condenser = 105degF, Superheat = 50degF, Subcooling = 15degF
The capacity was obtained by measuring the water loop temperature difference.
Capacity = 500 * GPM * (Water In - Water out)
(Heat pump in heating mode)
I did the same measurement on our older R22 units and the capacities of those units are very close to rated.
Right now I'm thinking its the compressor. So after the weekend I will try to build another unit with a Tecumseh compressor.
Would there be another reason for loosing capacity? I'm pretty sure the piping sizing is correct.
I appreciate your help. Let me know if you need any other info.
Reds
-
30-01-2010, 08:27 PM #5
Re: Compressor Capacity Troubleshooting Help
Did you measure GPM?... or use an estimate?
-
30-01-2010, 08:42 PM #6
-
30-01-2010, 09:42 PM #7
Re: Compressor Capacity Troubleshooting Help
Also, at moment we don't have any measured readings as yet from what I can see.
In one post you stated the evaporator and condenser temperatures as measured and in the second you state that they are design.
Have you got exactly the design operating conditions?
Your subcooling seems as per spec but the superheat is way off.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
31-01-2010, 03:07 PM #8
Re: Compressor Capacity Troubleshooting Help
The measured evaporator and condenser temperatures were +/- 3%
Flow was measured with a turbine type flow meter.
The only measurement that was off was the superheat. I will try to adjust it higher before I try changing compressors but I don't think it will increase performance much.
Thanks.
Similar Threads
-
need troubleshooting charts
By mcm12263 in forum New to REReplies: 1Last Post: 13-05-2009, 10:19 PM -
troubleshooting books
By marc5180 in forum Refrigeration BooksReplies: 42Last Post: 04-04-2009, 06:08 PM -
Daikin VRV Troubleshooting
By ral in forum FundamentalsReplies: 6Last Post: 30-09-2008, 08:36 PM -
Troubleshooting a vacuum pump and gauge set.
By Old Codger in forum FundamentalsReplies: 7Last Post: 08-08-2008, 05:13 PM -
Looking For A Good Troubleshooting Guide
By nightranger121 in forum Trouble ShootingReplies: 10Last Post: 23-11-2007, 06:16 PM