    Problems with a Hitachi 4001SCH Compressor



    HI I wonder if anyone could help. I have a Hitachi 4001SCH Screw compressor on a 1993 Hitachi Chiller, running on R22. On start up the compressor pulls 16 amps and slowly ramps up to 75 amps full load over a period of 30 minutes or so. This is a old chiller and works on a primitive loading and unloading system. However test have proved that there is no power to the unloading solenoids, there doesn’t feel that the solenoids are letting by, and the suction pressure is 5 bar, discharge 15 bar at low amps but then at full load amps of 75 amps drops to 12 bar with a SP of 4 bar. on low amps there is limited cooling, however once full load has been reach full cooling. But I can’t see where the compressor is losing. Other things I have tried and tested, Compressor windings, Contactors, and electrical circuits. Liquid by pass appears to be intact and not letting by. The compressor is a rebuild, and was replaced by a and other in 2008. Any suggestions would be appreciated.



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Problems with a Hitachi 4001SCH Compressor

    Hello steve.

    Just a few observations.

    I'm not too sure I understand your problem.

    You say the comp runs and when it is fully loaded it
    runs with about 12b head and 4b back pressures?
    You say it takes about 30 mins to fully load but the loading mag valve is not energised?

    First thing is, if the system is running fine when fully
    loaded what is your concern?

    Secondly, How is it loading if the mag valves are not opperating?

    I know there are more questions but I think the
    logical aproach would be start with the control (loading / unloading) and take it from there.

    taz.

    .

  3. #3
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: Problems with a Hitachi 4001SCH Compressor

    Hi steve i don,t quite understand the question but when the solnoid valve coils are denergised the compressor is fully loaded,if you need any extra info on how the valves work to load and unload the slide valve ,let me know and i will explain in depth.

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Problems with a Hitachi 4001SCH Compressor

    Quote Originally Posted by Clive Robert View Post
    Hello steve,

    Maybe your problem can be solved if you call this no 832-369-8277. They are experts in repairing the Air Conditionings.

    Thanks
    Seems like they are experts at being on the wrong continents too!

Similar Threads

  1. Replies: 3
    Last Post: 29-10-2009, 09:41 PM
  2. [Autocascade] Only a project ATM
    By before in forum CPU Overclockers
    Replies: 1
    Last Post: 07-05-2009, 11:13 AM
  3. hitachi RAS-63CHA3 compressor
    By gazcull in forum Air Conditioning
    Replies: 1
    Last Post: 09-03-2009, 11:28 AM
  4. Compressor pumping efficiency
    By shogun7 in forum Fundamentals
    Replies: 0
    Last Post: 25-02-2004, 10:50 PM
  5. Compressor failure...... cause
    By herefishy in forum Technical Speculations
    Replies: 8
    Last Post: 06-12-2002, 12:15 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •