    Daikin ftx25 bvmb



    Folks

    I'm looking for a service manual for the above, the extranet doesn't seem to list it.

    The unit is faulting on insufficient charge, i have the correct charge in, unit runs for a few hours and trips out.

    al



  2. #2
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: Daikin ftx25 bvmb

    not sure about the model numbers but had a problem similer turned out the strainer next to expansion device was dirty

  3. #3
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Daikin ftx25 bvmb

    thanks for that TBC

    al

  4. #4
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin ftx25 bvmb

    Hi,
    I think you will have more luck if you search using the outdoor model number, after all it's an outdoor fault your looking at.

  5. #5
    Join Date
    Dec 2008
    Location
    Isle of Man
    Age
    55
    Posts
    42
    Rep Power
    0

    Re: Daikin ftx25 bvmb

    EEV or actuator possibly faulty

  6. #6
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin ftx25 bvmb

    Quote Originally Posted by coolhandlew View Post
    EEV or actuator possibly faulty
    Or thermistor out of calibration

  7. #7
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Daikin ftx25 bvmb

    Quote Originally Posted by coolhandlew View Post
    EEV or actuator possibly faulty
    if you have a UO fault you will want to check the resistance of the discharge thermistor and indoor coil thermistor.
    make sure it is still clipped onto the pipe, if the system does not see a rise in discharge temp with the comp running it can faut on this.
    Is the unit pumping down?
    Then make sure the expansion valve coil has not fallen off.
    You should be able to check the expansion valve to see if you have a temperature drop across it.

    If it is pumping down change the liquid line filter and expansion valve body.
    Look on the extranet under RKS - bvmb

  8. #8
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Daikin ftx25 bvmb

    Brunstar

    Thanks for that, checked the eev coil with another unit and found one circuit open, have swapped coils to see if fault shifts to the other unit, these are real head wreckers!! spose it's why we get paid so much.......

    thanks

    al

  9. #9
    Rayshew's Avatar
    Rayshew Guest

    Re: Daikin ftx25 bvmb

    Hi Folks We have 4 of these units in our house in Portugal and whilst we use them irregularly, mostly cooling, one of them has always been troublesome. Tried to switch on using the remote and nothing! tried other remotes and still the same. Everything fine when I use the manual settings.
    Before I launch into getting the usual rip off merchants over there involved, does anyone have an idea what might be the problem?
    Any help would be appreciated,thanks.

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin, Why do we bother?
    By gwilliamson in forum Air Conditioning
    Replies: 21
    Last Post: 02-02-2010, 09:38 AM
  3. Panasonic Urban rebadged Daikin
    By complete HVAC in forum Air Conditioning
    Replies: 0
    Last Post: 19-08-2009, 04:35 PM
  4. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  5. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •