    Suction Accumulator High Level Interlock



    I have a client who questions whether it is necessary to have a suction accumulator high level interlock with the reciprocating compressors on an ammonia system. He feels that if an emergency shutdown occurs and the king valve is closed he would rather the compressors continued to run and force liquid into the receiver. Once a high level is reached in the suction accumulator then the receiver will no longer feed the accumulator but the compressor/s will continue to run feeding the receiver.

    It seems to me that once the high level in the suction accumulator is reached, it is important that the compressor/s stop since the compressors could ultimately begin to suck liquid brought back via the suction line to the accumulator causing potentially severe damage to the compressor/s.

    Can anyone please claraify this for me??

    Thanks!



  2. #2
    Join Date
    May 2009
    Location
    Sydney
    Posts
    73
    Rep Power
    15

    Re: Suction Accumulator High Level Interlock

    Hi Larry. Yes you are right. It is very important to stop compressors and try to boil liquid out of accumulator as vapour. Reason for high level must also be investigated and corrected before restarting compressors.

  3. #3
    Join Date
    Oct 2009
    Location
    Australia
    Age
    52
    Posts
    24
    Rep Power
    0

    Re: Suction Accumulator High Level Interlock

    Larry,

    I agreed Greg, your clients idea is good in theory, however all that will happen is the liquid temp in your accumulator will drop to to negative 30(c) & make the liquid almost impossible to boil off.. Especiallily if it is insulated..

  4. #4
    Join Date
    Sep 2010
    Location
    United States
    Posts
    32
    Rep Power
    0

    Re: Suction Accumulator High Level Interlock

    Why even have a high level cut-out if you bypass it? If this is a two stage system then you could suggest a transfer pump that would relieve liquid back to the Inter-cooler or intermediate pressure vessel.

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Suction Accumulator High Level Interlock

    Quote Originally Posted by Terron View Post
    Why even have a high level cut-out if you bypass it? If this is a two stage system then you could suggest a transfer pump that would relieve liquid back to the Inter-cooler or intermediate pressure vessel.

    Check the date of the posts my friend.
    Grizzly

Similar Threads

  1. Copeland select 6
    By Copman in forum Tools and Calculators
    Replies: 9
    Last Post: 27-05-2010, 09:01 PM
  2. R290 Suction Scrubber HI Level
    By Knappyfro in forum Trouble Shooting
    Replies: 1
    Last Post: 28-11-2009, 05:15 PM
  3. "Unstable" Rack Receiver Liquid Level
    By chweber in forum Commercial
    Replies: 3
    Last Post: 09-02-2009, 08:58 AM
  4. Propane compressor suction drum level issues
    By inuendo in forum Trouble Shooting
    Replies: 8
    Last Post: 02-06-2008, 09:19 AM
  5. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •