The problem you are going to have is choosing adesign point for your cap. the nature of the hot water heating beast is that it is always in a wide range of flux (compared to say a fridge which generally is more stable once the cabinet is at the required temperature)
maybe you should look at a single pass water heating system, controled by head pressure, this will give you a constant to work with, so then you only have to optimised around SST.
I do not think you should use your sight glass at all to judge charge. The only benefit (excluding moisture) is to show that you have flow. (Gauges would show the same)
-
28-01-2010, 09:15 AM #2
Re: Expansion noise - capillary tube into evaporator
Your quite right that selecting charge on a sight glass in this system would be almost useless. But it does show what condition the refrigerant is at as it enters the tube and for research and cap size changes it can be very useful.
It would be great if one could buy a glass tube - say 300mm long - about the same diameter as the compressor discharge tube to see the refrigerant condition. What a tool that would be.
Chef
-
28-01-2010, 09:18 AM #3
Re: Expansion noise - capillary tube into evaporator
I think that this is the key, here. The varying heat-loads, on both the evaporator side & condenser side, keep the system in relative dis-equilibrium.
maybe you should look at a single pass water heating system, controled by head pressure, this will give you a constant to work with, so then you only have to optimised around SST.
I do not think you should use your sight glass at all to judge charge. The only benefit (excluding moisture) is to show that you have flow. (Gauges would show the same)
These RHVAC systems are a lot more sensitive than many folks would have us believe.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
28-01-2010, 12:36 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Expansion noise - capillary tube into evaporator
Maybe this article could have some interesting information.
-
28-01-2010, 12:57 PM #5
Re: Expansion noise - capillary tube into evaporator
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
28-01-2010, 01:28 PM #6
Re: Expansion noise - capillary tube into evaporator
Very interesting discussion.
I have learnt a few new things today.
I may add one thing concerning the noise.
1. would it be quieter if a few smaller diameter cup tubes will be instead of one large diameter?
2. Because the refrigerant is R 134a, in a short time it most likely will block the cup tube, my suggestion is to use a small 1\4 drier, size 052 and braze the cup tube to the 1\4 tube on the outlet.
And Des, how about some work today?
-
28-01-2010, 03:19 PM #7
Re: Expansion noise - capillary tube into evaporator
Interesting thought. I wonder if anyone has thoughts on this?
2. Because the refrigerant is R 134a, in a short time it most likely will block the cup tube, my suggestion is to use a small 1\4 drier, size 052 and braze the cup tube to the 1\4 tube on the outlet.
And Des, how about some work today?Last edited by desA; 28-01-2010 at 03:35 PM.
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
30-01-2010, 01:35 PM #8
Re: Expansion noise - capillary tube into evaporator
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
Similar Threads
-
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
Noise from shell and tube evaporator
By wilsoncheung in forum Trouble ShootingReplies: 8Last Post: 25-03-2009, 03:29 PM -
Capillary Tube Characteristics
By Chef in forum FundamentalsReplies: 9Last Post: 10-03-2009, 01:03 PM -
metric capillary tube
By tralex in forum FundamentalsReplies: 5Last Post: 21-02-2006, 06:57 AM