    404a / OFN



    i recently went to a job where the customer had switched the machine on and ran it for 3 days with ofn in it instead of 404a. what can be done to save it?



  2. #2
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: 404a / OFN

    Hello.
    Test the motor windings resistance, "high pot" - when it is cooled down, check oil level, make a short start with current measurement, if it is found that the motor had survived, complete all the necessary putting to work procedures on the machine.

  3. #3
    ROYHUNT's Avatar
    ROYHUNT Guest

    Re: 404a / OFN

    Thanks Yuri .
    The compressor was extremely hot.
    It was vacced out and then recharg but still extremely hot . would you expect the comp to be irreparably damaged

  4. #4
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: 404a / OFN

    if it was a new system you would expect the clixen or another overheat /overcurrent device to save the comp

  5. #5
    Join Date
    Oct 2004
    Location
    uk
    Age
    56
    Posts
    193
    Rep Power
    20

    Re: 404a / OFN

    3 days would probably cause irreprable? damage to the windings. there is no cure. it would cause the oil to breakdown and spread around the system depending on the oil recovery method. dare i ask why it wasn't locked off?

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: 404a / OFN

    Why did he?

  7. #7
    ROYHUNT's Avatar
    ROYHUNT Guest

    Re: 404a / OFN

    Thanks for the reply.
    It was switched back on after a pressure test, by one of the shop staff . They were told not to touch it by my colleague. I went there to repair the leak he found as he couldnt repair it there and then as it is in an airport and needed hot works permit to be issued first.
    He should have made it impossible to switch on though,
    once again
    many thanks
    roy

Similar Threads

  1. Which system is better R 404A or R 717?
    By smpsmp45 in forum Refrigerants
    Replies: 36
    Last Post: 25-08-2011, 01:42 AM
  2. Trouble with 404A system...Please Help
    By wllmwallace in forum Commercial
    Replies: 8
    Last Post: 06-04-2009, 11:54 PM
  3. 404a high pressure?
    By flyboy3b in forum Trouble Shooting
    Replies: 236
    Last Post: 01-09-2008, 05:18 AM
  4. Hubbard 404a
    By evanso in forum Commercial
    Replies: 1
    Last Post: 07-09-2007, 09:29 PM
  5. R 404a
    By Samarjit Sen in forum Refrigerants
    Replies: 59
    Last Post: 07-08-2007, 06:35 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •