Results 1 to 2 of 2
    frostice55's Avatar
    frostice55 Guest
    Daikin UH fault code
    After being call to a recent install of a 4MXS68 multi Daikin, the fault code UH appeared.
    any ideas on the cause ?
    Sep 2009
    Scotland
    374
    Re: Daikin UH fault code
    Quote Originally Posted by frostice55 View Post
    Hi I would suggest you check interconnecting wiring (crossed cable cores/piping wiring) & compatibility of outdoor/indoors.
    See below info from manual.
    UH error
    Malfunction Decision Conditions:
    • Operation halt due to the anti-icing function in other rooms
    • Operation halt due to unspecified internal and/or external voltages
    • Operation halt due to mismatching of indoor and outdoor units
    Supposed Causes:
    • Freeze protection (A5) function is active on another indoor
    • Wrong connections at the indoor unit
    • PCB wrongly connected
    A5 error (Freeze protection)
    Supposed causes:
    • Wrong wiring or piping
    • Ev malfunctioning in each room
    • Short-circuit
    • Indoor unit heat exchanger temperature thermistor abnormality
    • Room temperature thermistor abnormality