    room noise



    Hi
    We just complete a HVAC project.After running the AHU we find a major problems that in few room due to air flow it creating very high level of noise.I thing it is because of very high safety static pressure in the duct, Is there any way to reduce the level of noise in the duct,We used silencer in the duct line,Is there any other reasons which can create sound in the room.



  2. #2
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: room noise

    did you check the speed and volume of the air passing the AHU??

    ice

  3. #3
    Join Date
    Nov 2009
    Location
    Bangladesh
    Age
    37
    Posts
    17
    Rep Power
    0

    Re: room noise

    Yes i checked.it was 5000m3/h,and SP is 2000Pa

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: room noise

    What is air speed on grilles?

  5. #5
    Join Date
    Jan 2010
    Location
    Ireland
    Age
    45
    Posts
    18
    Rep Power
    0

    Re: room noise

    Hello

    Airborne noise can be generated in ductwork systems
    as a result of excessive air velcoities.

    If noise is emitted from the distribution ductwork, and the duct air velocity exceeds the recommended maximum levels, you could have a major problem.

    You could consider the following options;
    1. lag the duct with acoustic insulation - however retrofitting acoustic insulation has a limited effect.

    2. integrate acoustic insulation with ceiling system-it should help dampen breakout noise.

    3. measure the air flow rate at duct sections that are audible from within the occupied space - check measured air volumes against design and commissioning data, reduce if possible.

    If problem noise is occuring at the supply air terminal's, measure the face velocity.
    Typically, the maximum recommended face velocity for louvre faced diffucers, serving general open plan office area should not exceed c. 2.5m/s -so as to satisfy best practice room noise levels.

    Rather me than you.

Similar Threads

  1. Maneurop MT51HK4A - Freezer Room
    By Hatchy in forum Trouble Shooting
    Replies: 35
    Last Post: 09-08-2010, 12:10 PM
  2. Blind Cold room specs help
    By frostedflake in forum Trouble Shooting
    Replies: 5
    Last Post: 13-03-2009, 01:49 AM
  3. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Replies: 10
    Last Post: 28-05-2008, 01:08 AM
  4. Thawing Room (defrosting Room For Meat)
    By arunuae in forum Commercial
    Replies: 3
    Last Post: 09-02-2008, 09:24 AM
  5. Freezer Room Panels
    By Feeze in forum Technical Discussions
    Replies: 10
    Last Post: 22-04-2005, 05:58 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •