Results 1 to 6 of 6
  1. #1
    ikpucool's Avatar
    ikpucool Guest

    copeland semi hermetic run on



    hi all..I am new to this site and am trying to get an answer to a weird situation.
    I have a single phase compressor for a commercial refrigeration unit that continues to run briefly after shut down, and shakes a lot also. I've replaced the capacitors and potential relay, voltage is within rated and amp draw is also within rated..
    During operations the unit is quiet and amp draw normal, start up amp draw normal also.
    I am starting to think it may be due to worn bearings that allow crank shaft to shift upon de energizing voltage.....??????
    Any one have any ideas?? any help would be great
    thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: copeland semi hermetic run on

    Hi and welcome to the forum.

    What type of compressor is it?

    Some machines will run backwards during pressure equalization.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: copeland semi hermetic run on

    I would try turning it off by the main isolator to see if it still does it, i've seen faulty contactors and wiring faults do strange things.
    If it still does it then maybe its a mechanical problem, maybe its snaped a rod or something.

    I once had a condenser fan motor that run backwards for five seconds and off for ten then on again and this was due to faulty control circuit wiring.

    Jon

  4. #4
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: copeland semi hermetic run on

    Quote Originally Posted by ikpucool View Post
    continues to run briefly after shut down
    Could you define this statement?

    LLSV shutdown, T'stat shutdown, LPC shutdown, contactor shutdown....... etc.

    Also, give us the compressor model number.
    Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com

  5. #5
    ikpucool's Avatar
    ikpucool Guest

    Re: copeland semi hermetic run on

    Quote Originally Posted by powell View Post
    Could you define this statement?

    LLSV shutdown, T'stat shutdown, LPC shutdown, contactor shutdown....... etc.

    Also, give us the compressor model number.
    the compressor is shut down by contactor that controls one line of power.....second line is fed live at all times....the contactor is controlled by voltage from electronic controller....ive checked the contactor and contacts as well as voltage and all is checking out normally....this is what makes it a weird problem....
    copeland semi hermetic....not sure of m/n at time of this reply...sorry

  6. #6
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: copeland semi hermetic run on

    Quote Originally Posted by ikpucool View Post
    the compressor is shut down by contactor that controls one line of power.....second line is fed live at all times....
    I'll assume a H/K/EA or 3A (1/2 thru 3 HP) model that's 115v?

    Verify that neutral is connected to terminal "R" and the hot leg is connected to "2" (feeding the overload).

    Then verify that the contactor is breaking the "hot" leg.
    Last edited by powell; 28-01-2010 at 02:50 AM.
    Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com

Similar Threads

  1. oil level indication / sample port in hermetic compressor
    By friocold2008 in forum Supermarket Refrigeration
    Replies: 8
    Last Post: 17-11-2009, 10:30 PM
  2. DC Hermetic Compressors
    By riggsby in forum Air Conditioning
    Replies: 1
    Last Post: 18-01-2008, 06:19 PM
  3. do we need a hermetic or semi hermetic comp.?
    By duraid in forum Fundamentals
    Replies: 14
    Last Post: 17-04-2007, 05:52 PM
  4. Hermetic reciprocating versus hermetic scroll
    By Cofreth in forum Technical Discussions
    Replies: 26
    Last Post: 19-11-2005, 06:29 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •