30gx probleme
I am facing problem with Carrier chiller model 30gx227a0224nee . I've just change the CPM board of compressor A2. although the LED red flashlight turn on, the green one dosn't work and the compressor A2 dosn't run. It would be helpful if you send me the address of DIP swich on the CPM board and tell me why LED green flashlight dosn't work.
Thanks a lot
Farhang
-
23-01-2010, 04:39 PM #2
Re: 30gx probleme
Is the board set for the correct compressor?
Green LED shows a communication error, check fault codes.
Do you have a manual for the unit?
If not try here--
http://eto.carrier.com/lit.aspBrian - Newton Abbot, Devon, UK
Retired March 2015
-
23-01-2010, 06:43 PM #3
Re: 30gx probleme
Check dip switch settings on old CPM board then set new CPM the same. Then CPM will communicate
-
24-01-2010, 08:03 AM #4
Re: 30gx probleme
Dear Gibbo
I checked every thing and they all seem alright. communication between A2 and B1 is ok, A2 and A1 is ok, but again there is a problem in green flash and it dosen't work. I don't know what address should I give to the board? there are 8 dip swith and 4 more dip switch. could you please help me?
thanks in advance for your kind attention.
-
24-01-2010, 09:41 AM #5
Re: 30gx probleme
match your dip switch settings from the old board to the new board.
-
25-01-2010, 05:29 AM #6
Similar Threads
-
carrier 30gx oil separator heaters
By Coolie in forum Trouble ShootingReplies: 6Last Post: 12-05-2010, 05:58 PM -
Carrier Chiller 30GX Error Code
By sbkvelocity in forum Trouble ShootingReplies: 8Last Post: 07-03-2010, 02:57 AM -
30GX Carrier screw compressor
By malik55 in forum Air ConditioningReplies: 9Last Post: 19-04-2009, 12:16 PM -
Carrier 30GX control issues
By whoopy-do in forum Trouble ShootingReplies: 6Last Post: 03-11-2007, 12:05 AM