19-01-2010, 06:39 PM #1
How Can decrease the compressor capacity
I Have compressor which capacity 46.2 Kw , I need decrease the capacity to 42.6 Kw to matching with evaporator which capacity 42.6 Kw . What can I do ??
19-01-2010, 07:31 PM #2
Re: How Can decrease the compressor capacity
You dont need to do anything.
Your compressor is capaity is 8% more.
Its fine.
capacity will decrease as evaporating temp. will drop.
20-01-2010, 01:23 AM #3
As c-c says, it could probably be left well alone.
If you are concerned about matching & balancing, then you could look into installing a service valve in the suction line between evap & compressor. Set the valve during first operation, if required, then leave it alone after that.
Trimming of the evap can also be performed by backing off on the evap fan speed.Engineering Specialist - Cuprobraze, Nocolok, CD Technology