    r 404 A



    hI Guys. Can you tell me if a sisten filed With 404 has a leak i have to replace all the refrigerant quantity or i just refil the missing quantity. Best Regards.



  2. #2
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: r 404 A

    where on the system did it leak from how much does the system hold in total,if it leaked from liquid side top it up,if leaked in vapour side you may have to recharge

  3. #3
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: r 404 A

    .

    404 has a very low glide. Less than a degree I think and all commercial large systems in the UK supermarket trade have refrigerant added to them once the leak is repaired.

    It is a commercial descision. If you are dealing in 10's of Kg's per system then no ill effect would be noticed for the most part across most tempreature ranges between -35 and 0 deg C.

    With 404 you would only notice the difference if you were using it at extreem temps.

    If you ask me for the text book answer then it is a Zeotropic and it should be pulled and replaced with new if there is any doubt about its composition, but you don't want the text book answer you want an oppinion



    taz.

    .

  4. #4
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: r 404 A

    all the above,but i would be inclined to top up with r507,r404 is r507 with 3 parts of 134a added.only to enable the maker to get around the patent etc.507 is more beneficial in high ambient condensing
    mmm to beer or not to beer...........lets drink breakfast

  5. #5
    Join Date
    Mar 2007
    Location
    Huddersfield
    Posts
    26
    Rep Power
    0

    Re: r 404 A

    How much time have you got???? Top up!

  6. #6
    Join Date
    Oct 2004
    Location
    U.K.-London
    Posts
    144
    Rep Power
    20

    Re: r 404 A

    Quote Originally Posted by ice_p View Post
    How much time have you got???? Top up!
    And this is why F-gas regs are coming into force soon.
    To get rid of the cowboys who are too lazy to perform a proper repair.

    It is already illegal to top up without repairing the leak!

    If in doubt, take the refrigerant out!
    Never underestimate anybody, you never know when they will make you look like an idiot!

  7. #7
    chuckblouse's Avatar
    chuckblouse Guest

    Re: r 404 A

    I am looking for the proper procedure to replace an R12 system with a R404A system.

  8. #8
    Join Date
    Jan 2010
    Location
    wales
    Age
    56
    Posts
    55
    Rep Power
    15

    Re: r 404 A

    do it the correct way by the book less haslle no comebacks f-gas regs state system must run at max efficiency so you decide

  9. #9
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: r 404 A

    Quote Originally Posted by chuckblouse View Post
    I am looking for the proper procedure to replace an R12 system with a R404A system.
    You will need a new condensing unit.
    Compressor and condenser will need to be changed,

    The system have to be cleaned from mineral oil, a new TXV, drier and receiver.

    The suction line on R12 is usually too big for R404.

    Consider replacing the whole old unit to a new one.

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: r 404 A

    Quote Originally Posted by Coolie View Post
    And this is why F-gas regs are coming into force soon.
    To get rid of the cowboys who are too lazy to perform a proper repair.

    It is already illegal to top up without repairing the leak!

    If in doubt, take the refrigerant out!
    He didn't say he hasn't repair the leak
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Dec 2008
    Location
    bucuresti
    Age
    47
    Posts
    16
    Rep Power
    0

    Re: r 404 A

    Thanks guys I use 404 in a chiler
    mounted on an ice rink and has condenser leak. Leak will be repaired. Thank you very much for your advice

  12. #12
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: r 404 A

    I've repaired many a leak on supermarket systems that use R404A.

    Every time found and repaired the leak then top up as required. As others have said the glide is small so you can get away with it.

    Remember if the leak is in a liquid part then equal parts of the different gases will be lost.
    If the leak is where you have a liquid/gas mixture (i.e. evaporator or condensor) then you could well lose only a certian part of the mixture.

    So what happens if the leak is in a soley a gas part of the system?

    I've been told equal parts as per a liquid leak get lost, but to my mind the mixture isn't chemically bonded so more of one part could be lost.

    How do you chaps see it?

    Cheers,

    Andy
    Health and safety first..........unless I'm in a hurry.

  13. #13
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: r 404 A

    I think if its leaking when its gliding thats when it can leak in unequal parts so in the evap or condenser.

    If its a capillary system i'd put a fresh charge in but anything bigger i'd add to what was left in the system.

  14. #14
    Join Date
    May 2008
    Location
    midlands
    Age
    64
    Posts
    37
    Rep Power
    0

    Re: r 404 A

    up to 3kg then its a balance of probabilities to top up or replace, over 3kg then we all know what we have to do in the UK !!!!!

    Now if we were in differing parts of the world this thread would be over in seconds

  15. #15
    Join Date
    Apr 2009
    Location
    South Africa
    Age
    49
    Posts
    108
    Rep Power
    16

    Re: r 404 A

    The best way to see if your gas is still in speck is to boil off some liquid in a small container and measure the temperature at 0 psi, then take your temperature pressure ruler and see if the temperature are within 10% as per manufacturers specks. If not recover the refrigerant and replace with new charge. ( depending of total charge in system)