17-01-2010, 05:17 PM #1
Re: DX GSHP problems
The refrigerant mass was checked a few weeks ago, but i am not sure that it was done properly, by the tecnician.
there is is on the evaporator suction, but not at the TXV.
There is no glycol/water since it is DX
-
17-01-2010, 07:51 PM #2
Re: DX GSHP problems
-
17-01-2010, 08:03 PM #3
-
18-01-2010, 12:29 AM #4
Re: DX GSHP problems
Again, please.
GSHP = ground-source heat-pump, no? So you're going DX directly implanted in the ground, not the conventional circulating loop system.
There should be temp sensor somewhere - in the ground, otherwise you'll not be able to work out what is going on.
Could your ground temp have really dropped so low? I'd wonder about that.Last edited by desA; 18-01-2010 at 12:34 AM.
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )