    heat exchange unit won't stop



    Hello,
    I've got a HEIL HHP060 heat exchange unit outside that won't stop. The air blower inside follows the thermostat's command but it looks like the compressor keeps running; I've waited for more than 2hours and it just keeps running.
    It sounds like a contactor is stuck but based on the electrival diagram posted in the unit the contactor is whithin a capacitor. Is this possible and if so how can I test the capacitor to find out if it went bad? My ohmeter shows that all three connections of the capacitor are connected which I didn't expect if a contactor is embedded.
    I'v swaped out the thermostat just in case but that didn't help.
    Any suggestion? Am I focusing on a wrong issue?



  2. #2
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: heat exchange unit won't stop

    Clearly - welded contact in the relay.
    Relay is inside of the indoor unit.

  3. #3
    prg281's Avatar
    prg281 Guest

    Re: heat exchange unit won't stop

    Thanks Yuri.
    Is there a voltmeter / ohmmeter test i could perform to confirm the failure?

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: heat exchange unit won't stop

    If the relay is on but has no power feed from the thermostat to the coil then its stuck in, the relay is not in the capacitor.
    Your outdoor unit could have a short on it if the relay is off and its still running, (maybe fan running but not at full speed?)
    Best to turn it off at the disconnect and get a tech to look at it.

  5. #5
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: heat exchange unit won't stop

    Is there a voltmeter / ohmmeter test i could perform to confirm the failure?
    Supply input's resistance of any unit like this is hundreds/thousands ohms, now there should be only few ohms. Find the relay and check if this version is true.

    If yes,you may try to knock , carefully, at the relay, but better change it, and find out what had caused the too high current that had made the relay's contact stuck.

  6. #6
    prg281's Avatar
    prg281 Guest

    Smile Re: heat exchange unit won't stop

    Replacing the relay fixed it!

    Thanks again Yuri.

    Regards,

Similar Threads

  1. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  2. First post, please be nice, prob with heat mode
    By back2space in forum Air Conditioning
    Replies: 93
    Last Post: 28-06-2009, 09:18 PM
  3. LG heat pump problem
    By back2space in forum Heat Pumps
    Replies: 132
    Last Post: 01-02-2009, 11:23 PM
  4. Super efficient, low carbon footprint, etc etc - ideas?
    By Makeit go Right in forum Air Conditioning
    Replies: 8
    Last Post: 05-12-2007, 05:56 PM
  5. heat exchanger for small chiller
    By star882 in forum Fundamentals
    Replies: 4
    Last Post: 30-01-2007, 12:06 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •