    Fundamentals



    HI!
    We are working in a pharmaceuticals project.At that project we suggest a 100TR air cool type chiller and we decide, we will use chill water directly from chiller to AHU.But engineers and consultants of that pharmaceuticals are suggesting that first take chill water to a large tank from chiller then take those water to AHU,They telling us this is more effective because at that case they will able to use chill water for other purpose and quality of chiller will be improved.Are they right? According to me and our engineers,Chill water will loose heat and AHU performance will decrease.



  2. #2
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Fundamentals

    Hello.
    I believe they are right; the chiller's equipment would last longer as there would be less cyclings, and the chiller's work in general would be more efficient. Only the qwestion remains whether the chiller is able to also handle additional load, besides that of the AHU's.
    Last edited by Yuri B.; 15-01-2010 at 05:22 PM.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Fundamentals

    The buffer tank should not be an additional load as it will be well insulated.

    It is required to maintain steady conditions for the chiller.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Fundamentals

    Quote Originally Posted by Yuri B. View Post
    ...the chiller's equipment would last longer as there would be less cyclings, and the chiller's work in general would be more efficient. Only the qwestion remains whether the chiller is able to also handle additional load, besides that of the AHU's.
    I disagree this: if your chiller has capacity steps where the smallest step matches +/- the smallest load, then there will be now problem at all.
    Why will it be more efficient?
    Every unit is calculated with some margin and additionally for max load which rarely happens.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Fundamentals

    I see many two-compressors Climavenetas - without or with a small water receiver, and the both compressors come in at least fifteen times an hour. This is efficiency?
    Installations have been being made as cheap as possible.
    Last edited by Yuri B.; 18-01-2010 at 07:25 PM.

  6. #6
    Join Date
    Jan 2010
    Location
    Ireland
    Age
    45
    Posts
    18
    Rep Power
    0

    Re: Fundamentals

    Hi

    The primary reason for considering a buffer vessel is to reduce the number of times the compressor is engaged, thus prolonging the service life of the chiller.
    A number of factors should be considered when designing cooling water systems and and integrating buffer vessel.

    1. chiller characteristics - single stage or multi stage compressor. Singe stage invariably require buffers to inhibit cycling. multi-stage can regulate output to match load and may operate fine without a buffer.

    2. systems water content - the greater the systems water content (circuit pipework & heat exchangers), the less chance a buffer is required.

    Standing losses (cooling loss) for buffer vessels are normally low, providing they incorporate appropriate thermal insulation and are not oversized - They do not normally impose a load issue on the chiller.

    Based on your requirements, i.e production unit cooling and possibly low water content, I would recommend a buffer help limit compressor starts/hour.

    From an economic point of view, you could install many buffers for the price of replacing a single failed compressor.

    I hope this helps.

     

Similar Threads

  1. Fundamentals
    By moideen in forum Fundamentals
    Replies: 1
    Last Post: 03-02-2009, 06:13 PM
  2. basic fundamentals
    By Ray Ang SM in forum Fundamentals
    Replies: 4
    Last Post: 09-06-2008, 11:25 PM
  3. Refrigeration fundamentals guide
    By malik55 in forum Fundamentals
    Replies: 2
    Last Post: 06-02-2007, 03:35 PM
  4. pump fundamentals
    By DALO in forum Trouble Shooting
    Replies: 1
    Last Post: 04-03-2006, 07:17 PM
  5. Gravity separator fundamentals and design
    By aruiloba in forum Technical Speculations
    Replies: 1
    Last Post: 08-03-2005, 02:31 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •