    1 out of 5 working



    Hi all
    I have 5 hitachi RAS 4HG7E cond units and 5 RC1 4HG7E cass units in one office area all controlled by one controller, the 1st unit off the controller works in all mode's but only the fan's run on the other 4,All 5 work in test mode heating and cooling spoke to hitachi checked cable / changed controller and setting's still 4 non running's.
    Any ideas
    cheers
    peapod



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: 1 out of 5 working

    I'd be looking at the dip switch settings on all the units and the controller to make sure they are set for group control and are addressed correctly.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: 1 out of 5 working

    Have they worked in the past or is this a new install?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Oct 2009
    Location
    Yorkshire
    Posts
    6
    Rep Power
    0

    Re: 1 out of 5 working

    hi brian/monkey spanners
    The install is about 4 years old but i have not seen it run only been call to it a few days ago(new staff have just moved in so no history of the system) ,i have checked and changed the address but with no luck , I didn't see any dip switches for group setting.
    I will be going back on monday so i will double check for the dip switches
    cheers
    peapod

  5. #5
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: 1 out of 5 working

    I don't fit Hitachi stuff often so am not really familiar with it. I usually phone the manufacturers technical people with problems like this, if they know there stuff they will be able to point you in the right direction.

  6. #6
    Join Date
    Oct 2009
    Location
    Yorkshire
    Posts
    6
    Rep Power
    0

    Re: 1 out of 5 working

    Hi all
    Went back yesterday i had disconnected the system from the site BMS system last week(at the BMS station) but after speaking to hitachi yesterday they said to diconnect the bms plugs on the indoor pcb, it work's now
    thanks for your help
    pea pod

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: 1 out of 5 working

    There you go, it's easy when someone knows how.

    Thanks for the update.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Jan 2008
    Location
    Manchester, Uk
    Age
    53
    Posts
    57
    Rep Power
    17

    Re: 1 out of 5 working

    Hitachi's don't wanna work in cooling at ambient below -7 / -5 oC. They have dip settings on the outdoor pcb to override the ambient sensor, i think it's dsw1, switch 2, but would need to check. It's not something they advertise. The controller shows no fault, but the condensing unit won't run.

    The unit addresses are set at the controller, and need to be changed if an indoor board is replaced. Or maybe they were never set up when installed. Daikin Tech will advise if necessary, it is easy to do, i have it written down somewhere, if you get stuck.
    Last edited by andy c; 21-01-2010 at 08:17 PM. Reason: added sentence.

Similar Threads

  1. Replies: 20
    Last Post: 14-06-2009, 05:51 PM
  2. OIL SEPARATOR not working properly
    By PEPELEBU in forum Trouble Shooting
    Replies: 14
    Last Post: 05-05-2008, 04:16 PM
  3. working hours
    By jan behnke in forum Chit Chat & Service Stories
    Replies: 11
    Last Post: 17-07-2005, 12:31 PM
  4. is my fridge working properly?
    By vincec in forum Trouble Shooting
    Replies: 1
    Last Post: 15-01-2002, 09:55 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •