    Mr slim iced coil



    Hi all,

    I attended a call to heating not working in an office today, a Mr slim split, the outdoor coil has a iced up quite alot, I dont suspect the unit is low on gas but I didnt notice it defrost while I was there either. The ambient temp was around 0 degrees.

    Does this sound like a blocked coil? Or does it sound more like a defrost problem? I am back on the job tomorrow as today was just a quick visit before I left for home so havent carried out any tests as yet. Just thought I'd pick your brains on here first to help me out a great deal.

    Cheers Guys



  2. #2
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: Mr slim iced coil

    It sounds like a low gas problems, but it you'r shore it's not that the problem you might have problems with the temperature readings, or the sensors not making good contact

  3. #3
    Join Date
    Mar 2009
    Location
    united kingdom
    Posts
    81
    Rep Power
    16

    Re: Mr slim iced coil

    did you put gauges on and check charge this is normal in winter for the coil to ice up but not completly

  4. #4
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: Mr slim iced coil

    No this is next step really, I just took the cover off and had a quick check for oil patches ect on the pipework, for signs of a leak, It is iced up quite badly, how often does the defrost cycle on these units? is it hourly?

  5. #5
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: Mr slim iced coil

    mate wouldnt set my sights on a gas leak straight away. with weather like weve been having it may just be on full heating too long etc

    check the simple things first

  6. #6
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: Mr slim iced coil

    Yea this was my thought to, I was jus expecting it to of defrosted befpre it got as bad. I will give the coil a thorough check first once all the ice melts!

  7. #7
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: Mr slim iced coil

    Quote Originally Posted by thebigcheese View Post
    mate wouldnt set my sights on a gas leak straight away. with weather like weve been having it may just be on full heating too long etc
    A quality unit won't have the problem for "full heating too long" ,and it's a Mitsubishi not made in China (no offense the them).
    It should be able to work as long as it's needed, the only problem that might be is for the wind, or water dripping on the unit from somewhere.

    Widemouthed no pressure and making shore all temperature sensors at their place it's difficult to say.

    And if the ice isn't uniform (big diff) it's for shore a low gas problem

  8. #8
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: Mr slim iced coil

    "And if the ice isn't uniform (big diff) it's for shore a low gas problem"

    Thats a good point, The ice is uniform, so this would indicate even temperature in the coil which would point away from low charge really?

  9. #9
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: Mr slim iced coil

    That would point away but you need to confirm it with the pressure because it's just a rule of tomb not fail safe.

    And in this case i stick with the temperature sensors not managing to feel that the unit is icing up (excluding the pressure transducer because is almost never happening)

  10. #10
    Join Date
    Dec 2009
    Location
    canada
    Posts
    43
    Rep Power
    0

    Re: Mr slim iced coil

    Check to make sur it's not cause by water dripping from the roof or gutter then freeze up it happened to me but i had a good 2 inches thick ice in the buttom of the outside unit that blocked the dripping hole.

    Melted it with warm water, i'v put a cover over the unit without blocking the flow of air and everything is ok now.

  11. #11
    Join Date
    Dec 2009
    Location
    canada
    Posts
    43
    Rep Power
    0

    Re: Mr slim iced coil

    Quote Originally Posted by Buzzant View Post
    i'v put a cover over the unit without blocking the flow of air and everything is ok now.
    Of course it already had a cover but i put a plastich sheet over it so water slip instead of freesing up on the cold metal.

  12. #12
    Join Date
    Dec 2009
    Location
    canada
    Posts
    43
    Rep Power
    0

    Re: Mr slim iced coil

    here is a picture except i cut it a bit more in the back so it does not interfer with the flow

    http://img42.imageshack.us/img42/7302/img6222o.jpg

  13. #13
    Join Date
    Jun 2009
    Location
    Columbus Ohio
    Age
    55
    Posts
    169
    Rep Power
    15

    Re: Mr slim iced coil

    one of my units had this issue.. outside air-temp thermistor was bad.. it was reading 60 degrees f all the time no matter what the temperature was.. stupid chinese unit will NEVER defrost if ambient temp is above 55f.. even though 3 temp sensors on the coil were -20 f it still wouldnt defrost.. might want to check the ambient air temp sensor...
    -Christopher

  14. #14
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: Mr slim iced coil

    Just to confirm, this unit was not low on gas hooked the gauges up and have good pressures, unit now heating fine (raised ambient temperature)

Similar Threads

  1. About 2 stage coil
    By cstyx in forum Technical Discussions
    Replies: 3
    Last Post: 09-04-2009, 08:26 PM
  2. iced up evap coil
    By wilks in forum Fundamentals
    Replies: 6
    Last Post: 31-08-2007, 09:15 PM
  3. Dont be shy, advice needed.
    By Sledge in forum Air Conditioning
    Replies: 9
    Last Post: 27-06-2007, 03:09 PM
  4. Burst Coil
    By frank in forum Air Conditioning
    Replies: 13
    Last Post: 20-02-2005, 06:28 PM
  5. Article in ACH&R News
    By Gary in forum Fundamentals
    Replies: 8
    Last Post: 20-05-2003, 12:27 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •