    I am half way through replacing the compressor on a Lennox AHU Package unit. The unit has been off line for sometime now, I am just wondering how low ambient temperatures will affect the system as I am still fairly new to the trade.

    I have vac'd and refilled with ofn several times now to try and rid of any ice/moisture/particles ect



    Would it be good practise to leave the crankcase heater on for sometime before starting it up for the first time?

    I have no sightglass on the system so will have to weigh the charge in what sort of effect will the low ambient temp have on this?

    Sorry for all the questions, im still learning!



  2. #2
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: Changing Compressor Low ambient

    It depends on how low is inside the unit,and if you had any other problems beside the compressor change.

    Typically it is recommended to add some electrical heaters (temporary heat blowers) to heat the entire system, it's not enought only for the crankcase heater (depending on the actual ambient temp), and vac the system at the same time.
    if the pipe temperature is too low, you might vac forever and it not extract all of the moisture (depending on the repair that was done).

    And obligatory replace the filter dryer in case the unit is having one.
    And putting this all beside for the start u need the crankcase heater on for 6-8 hours (i do it for more than 12 hours) for the oil to be heated up.

    And for the weight, the refrigerant is having the same weight for any temperature/pressure for the same amount.

    wen you are charging the unit, make shore the liquid is not depositing in the compressor

  3. #3
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Changing Compressor Low ambient

    Would it be good practise to leave the crankcase heater on for sometime before starting it up for the first time?
    It is very good practice to have the crankcase heater on at all times when the comp. is not running (and even sometimes when it is)if the oil ever gets cold you should allow sufficient time for the heater to achieve the oils required standing temperature. Most manufacturers say a flat time of 12 Hrs but the bigger comps could be 24 Hrs+.

    Filling by weight (especially on packaged units) is the prefered way.
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  4. #4
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: Changing Compressor Low ambient

    Cheers guys, I have changed the drier yes I am just worried there still mite be ice in there as since I started the job its bearly reached above freezing! I will have to source some type of heaters.

    The reason I changed the compressor, the previous was taking out the main mcb, a winding was down, before the compressor failed it was making dodgy sounds like moisture was in there.

    How long would be advised to vac for while heating?

  5. #5
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: Changing Compressor Low ambient

    Depends on the size of the unit, and if you can cover it all up with foil or something to keep the heat inside and the temperature you manage to get inside, you might get away with 1-2 hours at 30 deg C, but the unit size is important

  6. #6
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: Changing Compressor Low ambient

    Cheers mate,

    Its not too big its a package unit with 7.71kg charge of 407c H.5ft W.4ft L.6ft

  7. #7
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: Changing Compressor Low ambient

    Then yes , 1-2 hours if you manage to lift the temperate should be enough

Similar Threads

  1. Low ambient temperature breaking Beko?
    By idontlikecoffee in forum Domestic
    Replies: 3
    Last Post: 10-03-2009, 01:21 PM
  2. ambient temp effect on chillers operation
    By fridgeilliterat in forum Fundamentals
    Replies: 7
    Last Post: 25-01-2009, 10:54 PM
  3. Air Cooled Mono Block Units & high Ambient
    By smpsmp45 in forum Technical Discussions
    Replies: 4
    Last Post: 11-12-2007, 06:29 AM
  4. 404A head pressure to ambient rule of thumb
    By kengineering in forum Refrigerants
    Replies: 22
    Last Post: 08-05-2007, 10:40 PM
  5. Ambient and Condensing.
    By kfjoe in forum Fundamentals
    Replies: 9
    Last Post: 07-02-2004, 04:31 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •