    Fundamentals



    Hi!
    Our Clint has a trane 100TR chiller.What is the maximum quantity of cold air(In CFM) they can get from that chiller. Is there any rule to find out the quantity of air from chiller capacity.



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Fundamentals

    You can get an unlimited amount of cold air from that chiller the only limitation would be the fancoil(s) you connected to it.

    Say that it's installed up by the north pole...


    Nah we need a bit more info I'm afraid:
    First, we are talking about a chiller i.e. a machine that cool water or another fluid?
    If so what are used to exchange heat with the air?
    Cold air? What we need to establish is your expected temperature differential. I.e. if the air going in to the unit is 30˚C then what do you expect the air leaving the unit to be.
    What ambient conditions are we expecting this unit to operate under?
    And
    So
    On.

Similar Threads

  1. Fundamentals
    By moideen in forum Fundamentals
    Replies: 1
    Last Post: 03-02-2009, 06:13 PM
  2. basic fundamentals
    By Ray Ang SM in forum Fundamentals
    Replies: 4
    Last Post: 09-06-2008, 11:25 PM
  3. Refrigeration fundamentals guide
    By malik55 in forum Fundamentals
    Replies: 2
    Last Post: 06-02-2007, 03:35 PM
  4. Probably the most basic of fundamentals
    By shoot_j in forum Fundamentals
    Replies: 8
    Last Post: 01-01-2007, 10:40 AM
  5. Gravity separator fundamentals and design
    By aruiloba in forum Technical Speculations
    Replies: 1
    Last Post: 08-03-2005, 02:31 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •