Thread: Carrier Chiller
12-01-2010, 07:03 PM #1
Carrier Chiller
Hi, Iam having problems with oil pressure on a Global GX series chiller with screw compressors.I have replaced the external oil filter but I think I need to replace the internal filter.
Does anyone know how this is accessed please ?
12-01-2010, 07:27 PM #2
Re: Carrier Chiller
Assuming that you mean the 30GX series then the filter is behind the plug.
Useful? no probably not.
Have a read of the manual from Carrier and look on page 38.
http://eto.carrier.com/litterature/i...30GX_HX_LR.pdfBrian - Newton Abbot, Devon, UK
12-01-2010, 08:27 PM #3
Re: Carrier Chiller
hi colin you need a 19mm alan key on a 1/2 inch socket to open the round plug, and then a long nose pliers to pull the internal filter out,
18-01-2010, 10:40 AM #4
Re: Carrier Chiller
Isolate the oil line at the separator. You will need to bleed the oil pressure off through the access port at the compressor. If it doesn't bleed off, then you have to drop the refrigerant charge. With the pressure bled off, there is a 3/4 inch allen key fitting on the compressor at the top, uncrew it and the ineternal filter is behind that, just be careful how you remove it and then change, screw back in, evacuate the oil line open it up and start the machine. The oil pump will develop enough pressure to start, easy as that.
a problem shared is a problem halved
19-01-2010, 08:12 AM #5
Re: Carrier Chiller
Internal oil filter is at top of compressor just beside the terminal box, you will need a 19mm alan key or socket to remove simply turn off machine purge any pressure from the shrader directly next to the cover then you can safely remove it.
Alternatively call a Carrier Service Department
01-02-2010, 05:08 AM #6
its hard to get to
also does anyone know how to make a mod for vacuum forming plastic
also using spray in insulation
and what would be a good liner for a wooden barrel?Last edited by chillin out; 06-02-2010 at 02:27 PM.
Carrier chiller basic board problem
By noushad123 in forum Trouble ShootingReplies: 25Last Post: 17-06-2010, 06:55 AM -
Carrier Brine Chiller
By charlie n in forum IndustrialReplies: 6Last Post: 08-01-2010, 08:54 AM -
Carrier Chiller Help
By superswill in forum Trouble ShootingReplies: 7Last Post: 18-01-2007, 10:06 PM -
Carrier chiller oil migration
By lowtech in forum IndustrialReplies: 5Last Post: 30-04-2006, 04:11 PM