    Low ambient Temps & Outside Air Cooled Condensers!



    Hi Guys.
    Because of the abnormally prolonged cold spell we have been having.
    We have been getting a large amount of issues with plant. That is directly related to the system pressures being lower in the Condenser than the evaporator.
    For instance, causing Liquid migration into the condenser with the subsequent L.P. issues upon start-up etc.
    I was just wondering how for those of us that work in more extreme Cold climates get over this problem?
    Grizzly



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Low ambient Temps & Outside Air Cooled Condensers!

    Quote Originally Posted by Grizzly View Post
    Hi Guys.
    Because of the abnormally prolonged cold spell we have been having.
    We have been getting a large amount of issues with plant. That is directly related to the system pressures being lower in the Condenser than the evaporator.
    For instance, causing Liquid migration into the condenser with the subsequent L.P. issues upon start-up etc.
    I was just wondering how for those of us that work in more extreme Cold climates get over this problem?
    Grizzly

    Just open the fridge door and let the heat out

    taz

    .

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Low ambient Temps & Outside Air Cooled Condensers!

    I used to get problems with ice bank milk tanks in the winter, especially when they had heat recovery tanks on them.
    Farmer would use all the hot water to wash the milking parlour, which would then be replaced by cold which would result in the refrigerant sitting in the heat recover, condenser and reciever and the unit going off on LP.

    Bucket of hot water over the TXV and bulb to get some refrigerant into the evap, sack on the condenser, and away she went

    Once it had been running for a while and got some heat in the system it would be ok.

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Low ambient Temps & Outside Air Cooled Condensers!

    Is the liquid draining back to the receiver, or is it stacking up in the condenser?

    This is a common problem since you can't build discharge pressure to push liquid to the evaporators, right?

    About the only to get the system running is to shut down the fans and valve off all of the coils except for one, and hope that works.
    If all else fails, ask for help.


  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Low ambient Temps & Outside Air Cooled Condensers!

    I'd go with monkey spanners,

    hot water will do the trick.

    You can also operate it with a SV which is controlled by low discharge and a spraying nozzle.

  6. #6
    M.Nadeem's Avatar
    M.Nadeem Guest

    Arrow Re: Low ambient Temps & Outside Air Cooled Condensers!

    Quote Originally Posted by Grizzly View Post
    Hi Guys.
    Because of the abnormally prolonged cold spell we have been having.
    We have been getting a large amount of issues with plant. That is directly related to the system pressures being lower in the Condenser than the evaporator.
    For instance, causing Liquid migration into the condenser with the subsequent L.P. issues upon start-up etc.
    I was just wondering how for those of us that work in more extreme Cold climates get over this problem?
    Grizzly
    Hi:- if condensor is air forced then u can use one fan cycling switch to mantain the discharge pressure . hope it will help you.
    Nadeem

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Low ambient Temps & Outside Air Cooled Condensers!

    Thanks for all the input guys.

    Taz.
    I love your humour! Sadly the type of equipment I am talking about doesn't normally have Doors!
    MS and Iceman you are both spot on with ways of getting around this problem.
    I have used a variety of the above options to good effect and yes Iceman.
    I was basically refering to the problem of lack of lift across the comp. Low Suction Pressures etc upon start up once the refrigerant has migrated into the Condenser.
    Mike and M.Nadeem thank you also!
    Basically I know how we have gotten around it this time!
    But where it would happen more frequently has anyone developed a remedy?
    Just wondered that was all!
    Cheers Grizzly

  8. #8
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Low ambient Temps & Outside Air Cooled Condensers!

    On another site, this time with a DX milk tank, compressors mounted on the tank but with remote condensers and no recievers and on pumpdown cut out.
    This used to trip the LP switch on frosty mornings but by the time we had got to site the sun had been on the condensers and it would fire up ok (often they will start milking at 4-4.30am

    I did toy with the idea of fitting a three minute time delay to the LP switch (linked in with the solenoid so it only worked when it was open) but the problem went away with the warm weather, and the customer has now retired.

  9. #9
    haree's Avatar
    haree Guest

    Re: Low ambient Temps & Outside Air Cooled Condensers!

    all ideas good!

  10. #10
    Join Date
    Aug 2007
    Location
    UK
    Age
    42
    Posts
    135
    Rep Power
    17

    Re: Low ambient Temps & Outside Air Cooled Condensers!

    Condenser fans on VFD. Install a small dry cooler with pump.
    The Bridge Keeper
    'Answer me these questions three, n'er the other side ye see.'
    What is your name?
    What is your favourite colour?
    What is your suction superheat?

  11. #11
    Join Date
    Jan 2009
    Location
    sunny norfolk
    Posts
    81
    Rep Power
    16

    Re: Low ambient Temps & Outside Air Cooled Condensers!

    i was working on a 20kw water chiller yesterday with the same problem. i ended up putting a fan speed controller on the condenser. not cheap as it was 3 phase but has sorted the problem

  12. #12
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Low ambient Temps & Outside Air Cooled Condensers!

    Drain the water from basin and cycle fans only. A Russian trick I learnt, don;t forget to isloate the spray pump.

  13. #13
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Low ambient Temps & Outside Air Cooled Condensers!

    whack a fan heater in it and cycle cond fan
    mmm to beer or not to beer...........lets drink breakfast

  14. #14
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: Low ambient Temps & Outside Air Cooled Condensers!

    Quote Originally Posted by HallsEngineer View Post
    Condenser fans on VFD. Install a small dry cooler with pump.

    im sure tescos would pay for this! good idea all the same!

  15. #15
    Join Date
    Jan 2007
    Location
    scotland
    Age
    46
    Posts
    159
    Rep Power
    18

    Re: Low ambient Temps & Outside Air Cooled Condensers!

    ive had a few problems with the cold spell one store ambient temp was -16 during the day those searle cond units are a real pain as the fan speed controllers wont stop,had to go around fitting hp switches to cut out when hp dropped below 9br.had one store where the condensors had sucked in that much snow that they had iced up.

  16. #16
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Low ambient Temps & Outside Air Cooled Condensers!

    Quote Originally Posted by Magoo View Post
    Drain the water from basin and cycle fans only. A Russian trick I learnt, don;t forget to isloate the spray pump.
    Water from the aircooled condenser?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  17. #17
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Low ambient Temps & Outside Air Cooled Condensers!

    Refac used to bridge the LP for some time ( +/-20 seconds) after startup to allow pressure buildup on the high side.
    With extreme cold conditions, how I should do it?
    Install an additional condenser inside the building because I suppose this waste heat can be used usefully inside the building if it's really that cold. And then bypass proportionally the additional excess heat to the outside condenser.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  18. #18
    coelhinho78's Avatar
    coelhinho78 Guest

    Re: Low ambient Temps & Outside Air Cooled Condensers!

    yep thats it, you can use a themoetactic tree way valve to control it

  19. #19
    Join Date
    Jan 2010
    Location
    Christchurch
    Age
    54
    Posts
    28
    Rep Power
    0

    Re: Low ambient Temps & Outside Air Cooled Condensers!

    This is a common problem in the south island of new zealand during winter, putting the condenser fans on a pressure switch helps but wont aid you during start up, Danfoss manufacture a wintering valve which maintains pressure in the high side keeping it high enough for start ups, bridging the LP helps but you don't really want it to run in a vacuum to long either.

Similar Threads

  1. Stal Water Cooled Shell & Tube Condensers
    By Samarjit Sen in forum Commercial
    Replies: 2
    Last Post: 18-02-2009, 01:46 AM
  2. Replies: 9
    Last Post: 30-01-2009, 07:50 AM
  3. Air Cooled Mono Block Units & high Ambient
    By smpsmp45 in forum Technical Discussions
    Replies: 4
    Last Post: 11-12-2007, 06:29 AM
  4. Replies: 10
    Last Post: 18-03-2006, 07:35 PM
  5. water cooled condensers
    By aaron crimmins in forum Fundamentals
    Replies: 2
    Last Post: 22-07-2002, 04:24 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •