12-01-2010, 02:30 AM #1
Equalization problem
Friend had a question, working on a home built liquid chiller using a TXV.
Has an external equalizer, but seems to not be equalizing enough after shut down to allow a reboot with plenty of time.
Any thoughts?
-
12-01-2010, 02:39 AM #2
Re: Equalization problem
I presume you mean "external equaliser" is on TXV, if so, not there to equalise the system, Add anti-cycle timer or change starting method (i bet you are using a PSC start) or add a unload solenoid valve (between suction and discharge)
-
12-01-2010, 03:26 AM #3
Re: Equalization problem
Ah yes my bad, does a system like this actually require a solenoid to unload?
-
12-01-2010, 03:46 AM #4
-
12-01-2010, 04:03 AM #5
Re: Equalization problem
What info would help?
1hp LG Rotary
2.3kw Condenser coil with fan
30 plate HX
Danfoss TES2 with 01 Orifice
R404a
-
12-01-2010, 04:29 AM #6
-
12-01-2010, 05:37 AM #7
Re: Equalization problem
PSC, so yeah just a run cap.
And single phase.
But shouldnt the system be equalizing completely when its off?
-
12-01-2010, 07:42 AM #8
-
12-01-2010, 06:08 PM #9
Re: Equalization problem
Is there any way to tell which kind of TXV allows this and which don't? I've never seen this, but I normally only work on systems with EEV and captubes.
Similar Threads
-
MFI AMP6855 defrost problem
By gliderpilot47 in forum DomesticReplies: 4Last Post: 12-01-2011, 12:11 PM -
problem with GE air con power problem
By Richie101 in forum Air ConditioningReplies: 6Last Post: 05-11-2009, 04:00 PM -
Samsung Vivace Problem AQV24VBCN
By goldpau in forum Air ConditioningReplies: 0Last Post: 18-09-2009, 06:28 PM -
Saunier Duval Problem
By mallorcanangel in forum Air ConditioningReplies: 1Last Post: 10-07-2009, 01:26 AM -
Furance problem
By ALONEI in forum Trouble ShootingReplies: 10Last Post: 14-05-2008, 11:32 AM