    Equalization problem



    Friend had a question, working on a home built liquid chiller using a TXV.

    Has an external equalizer, but seems to not be equalizing enough after shut down to allow a reboot with plenty of time.

    Any thoughts?



  2. #2
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Equalization problem

    I presume you mean "external equaliser" is on TXV, if so, not there to equalise the system, Add anti-cycle timer or change starting method (i bet you are using a PSC start) or add a unload solenoid valve (between suction and discharge)

  3. #3
    Join Date
    Jul 2007
    Location
    Flemington, NJ
    Posts
    21
    Rep Power
    0

    Re: Equalization problem

    Ah yes my bad, does a system like this actually require a solenoid to unload?

  4. #4
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Equalization problem

    Quote Originally Posted by NoL View Post
    Ah yes my bad, does a system like this actually require a solenoid to unload?
    No not really, we need more info

  5. #5
    Join Date
    Jul 2007
    Location
    Flemington, NJ
    Posts
    21
    Rep Power
    0

    Re: Equalization problem

    What info would help?


    1hp LG Rotary
    2.3kw Condenser coil with fan
    30 plate HX
    Danfoss TES2 with 01 Orifice
    R404a

  6. #6
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Equalization problem

    Quote Originally Posted by NoL View Post
    What info would help?


    1hp LG Rotary
    2.3kw Condenser coil with fan
    30 plate HX
    Danfoss TES2 with 01 Orifice
    R404a
    Do not know exact machine single phase?, but, is it a Permanent Split Capacitor Compressor (PSC)?, these have little starting torque, change for a relay and start capacitor. or unloading valve, or larger anti cycle time.

  7. #7
    Join Date
    Jul 2007
    Location
    Flemington, NJ
    Posts
    21
    Rep Power
    0

    Re: Equalization problem

    PSC, so yeah just a run cap.
    And single phase.
    But shouldnt the system be equalizing completely when its off?

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Equalization problem

    Quote Originally Posted by NoL View Post
    PSC, so yeah just a run cap.
    And single phase.
    But shouldnt the system be equalizing completely when its off?
    Depends on the type of TXV fitted.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Jul 2007
    Location
    Flemington, NJ
    Posts
    21
    Rep Power
    0

    Re: Equalization problem

    Is there any way to tell which kind of TXV allows this and which don't? I've never seen this, but I normally only work on systems with EEV and captubes.

Similar Threads

  1. MFI AMP6855 defrost problem
    By gliderpilot47 in forum Domestic
    Replies: 4
    Last Post: 12-01-2011, 12:11 PM
  2. problem with GE air con power problem
    By Richie101 in forum Air Conditioning
    Replies: 6
    Last Post: 05-11-2009, 04:00 PM
  3. Samsung Vivace Problem AQV24VBCN
    By goldpau in forum Air Conditioning
    Replies: 0
    Last Post: 18-09-2009, 06:28 PM
  4. Saunier Duval Problem
    By mallorcanangel in forum Air Conditioning
    Replies: 1
    Last Post: 10-07-2009, 01:26 AM
  5. Furance problem
    By ALONEI in forum Trouble Shooting
    Replies: 10
    Last Post: 14-05-2008, 11:32 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •