    Daikin uatyp180amy1



    hey fellas been working on a system but want to give you fellas a few figures and see what you guys think! Model number as above and on R407c,4.3kg

    Heat mode

    Discharge pressure=16 bar
    Suction pressure=2.5bar
    Air on evap= 17.0
    Air off evap=30.5
    Air on condenser=2
    Air off condenser= 0
    Temp going into evap=56 deg c
    Temp out of evap= 24 deg c
    Temp going into expansion valve=24 deg c
    Temp out of expansion valve=7 deg c
    Temp into condenser=7 deg c
    Temp out of condensor= 2 deg c
    Suction into compressor= 3 deg c


    cooling mode

    Discharge pressure=12 bar
    Suction pressure=3 bar
    Air on evap=18 deg c
    Air off evap=6
    Air on condenser=20 deg c
    Temp going into evap= -2 deg c
    Temp out of evap= 5
    Temp goin into expansion valve= 27 deg c
    Temp out of expansion valve= -2 deg c
    Temp into condenser=57 deg c
    Temp out of condenser=27 deg c
    Suction into compressor=9 deg c

    much appreciated

    adam


    ajj

  2. #2
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Daikin uatyp180amy1

    What do you want to know?
    The difference between genius and stupidity is that genius has its limits.

    Marc

  3. #3
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Daikin uatyp180amy1

    You got a lot of superheat at the comp suction in cooling mode are you sure that the system was in stable operation when you took the measurements
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  4. #4
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin uatyp180amy1

    Quote Originally Posted by TRASH101 View Post
    You got a lot of superheat at the comp suction in cooling mode are you sure that the system was in stable operation when you took the measurements
    Airconadam,

    Does the unit have a fan speed controller option installed? The min operating range (ambient temp) in cooling is 20 C without HPC.
    Last edited by VRVIII; 13-01-2010 at 09:59 AM.

  5. #5
    Join Date
    Feb 2007
    Location
    north west
    Age
    36
    Posts
    243
    Rep Power
    18

    Re: Daikin uatyp180amy1

    hi yes the outdoor did have a fan speed controller but was only coming on every 10 secs and then stopping and continue to do so,I thought due to the low head pressure? it was set to the auto position.We have been having problems with this unit with it going off on hp but only on heating? I think possibly an airflow problem. thanks alot

    adam
    Last edited by airconadam; 13-01-2010 at 08:30 PM.
    ajj

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin FDYQ250M
    By carl in forum Air Conditioning
    Replies: 7
    Last Post: 11-08-2009, 12:56 AM
  3. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  4. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM
  5. Daikin Comp and inverter
    By WCC73 in forum Air Conditioning
    Replies: 5
    Last Post: 08-11-2008, 08:44 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •