11-01-2010, 08:01 AM #1
legal 101 gas leak check
CUSTOMER (SHOP WITH LITTLE MONEY!!) has an undersized fujitsu heatpump 7kw r22 cassette which in the recent cold snal heats for 45 min or so, stops on fault code (000 00...no fault) Then can be restarted.. Air off cassette is 35 degrees room is 12 degrees ambient is minus 1. As I see it the fault is either 1 a fault 2 just the unusual conditions 3 low gas. If the conditions were hotter I would set it in cooling and have a feel for temps and pressures but I cant do this due cold. Logically easiest thing to do is trell cust to wait till its warmer to check the system. HOWEVER am I right in thinking that due fgas regs As there is a POSSIBILITY of a gas leak I have to tell the customer to immediately make the system safe and check for leaks. (recover press test check... expensive) An opinion as to what very low temps might do to a fixed speed heatpump which would shut the system down on a fault code which dissapears (000 00) before the system can be interogated welcome. Liquid back to comp that dissapears?? High pressure trip and reset?? Any opinions on the legal and practical aspect welcome please.
-
11-01-2010, 09:01 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: legal 101 gas leak check
35°C-12°C is 23K dt and with 930m^3/h (indoor fan high) that is 7,4 kW emitted heating power.
Looks like perfectly healthy AC if that temperatures are measured at indoor fan at high.
What is full model #?Last edited by nike123; 11-01-2010 at 09:40 AM.
-
11-01-2010, 09:14 AM #3
Re: legal 101 gas leak check
model is auy25R cassette
Similar Threads
-
Mitsubishi Gas leak? PURY P250 YGMA
By marc5180 in forum Air ConditioningReplies: 82Last Post: 31-12-2010, 07:28 PM -
Evasive gas leak
By Feeze in forum Technical DiscussionsReplies: 24Last Post: 18-08-2008, 07:22 AM -
Help!!! Shell and Tube Evap Leak
By tommy Gun in forum Trouble ShootingReplies: 7Last Post: 22-07-2007, 12:45 PM -
Air conditioning maintenance procedure
By Andy T in forum Air ConditioningReplies: 12Last Post: 27-05-2006, 06:57 PM -
Leak check dye
By Rango in forum Tools and CalculatorsReplies: 4Last Post: 05-02-2004, 11:11 PM