    TXV/TEV equalizing line size?



    Whats the correct size for these lines? they are all 1/4" on the valves and i have seen them piped in 1/4" and in 1/8" as well.

    Usually i just get one of those ready made coiled copper pressure switch lines and cut it in half to use as an equalising line, any thoughts on whether i should be making up a propper 1/4" one instead of being lazy

    Jon



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: TXV/TEV equalizing line size?

    Quote Originally Posted by monkey spanners View Post
    Whats the correct size for these lines? they are all 1/4" on the valves and i have seen them piped in 1/4" and in 1/8" as well.

    Usually i just get one of those ready made coiled copper pressure switch lines and cut it in half to use as an equalising line, any thoughts on whether i should be making up a propper 1/4" one instead of being lazy

    Jon

    Hi mate.

    It is only an equalising line.
    Refrigerant does not flow through it, it only transfers the pressure from one end to another.

    So I do not think the diamiter of the pipe maters too much.
    On an internal equalised valve the ballence port is only 1 mm in diameter.

    Cheers taz.

    .

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: TXV/TEV equalizing line size?

    Cheers Taz,

    Thats what i thought. I did wonder though if the smaller bore pipe would be likely to get blocked with oil, especially in freezer aplications.

    Jon

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: TXV/TEV equalizing line size?

    Hi Jon,

    Just like you I'm being lazy, with one small difference, I have them prepared shorter - 60cm long.

    Never had any problems in TEV performance.

  5. #5
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: TXV/TEV equalizing line size?

    Equalizer line has no flow (well it should not) and only sensors pressure, so line size itself is not important, I do exactly what you do, cut a pre made pressure couple in half, if no flare is required, I just use capillary of a similar size.

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: TXV/TEV equalizing line size?

    I'm with taz. I normally use 6mm flexible capillary hose.

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: TXV/TEV equalizing line size?

    I agree with No Nick and MF. But if external is frosted the TX is by-passing through pushrods . A common problem with Sporlan TEXV's.
    magoo

  8. #8
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: TXV/TEV equalizing line size?

    Cheers guys,

    Now let just say a valve has just started passing by into the equalizing line, now if its been piped with small bore that can't flow enough to stop the pressure rising at the txv, will this cause the valve to open up to try and match the temperature at the bulb to the now false pressure at the txv?

    Jon

  9. #9
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: TXV/TEV equalizing line size?

    I've had a think about it and plotted some pressure and temperature on a graph and now think this will cause the valve to shut down as it will lower the percieved superheat.

    I shall be interested to here what you guys think

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: TXV/TEV equalizing line size?

    Quote Originally Posted by monkey spanners View Post
    Cheers guys,

    Now let just say a valve has just started passing by into the equalizing line, now if its been piped with small bore that can't flow enough to stop the pressure rising at the txv, will this cause the valve to open up to try and match the temperature at the bulb to the now false pressure at the txv?

    Jon
    Jon, this is a fault. You may want to guarantee fault tolerance to the system and clearly, the smaller the capillary, the higher chance of reevaporating the spilled liquid, but you will easily detect the fault by noticing the formation of ice around the capillary.

  11. #11
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: TXV/TEV equalizing line size?

    Cheers NoNickName,

    I'm just wondering what effects having a txv leaking down the equalizing line will have on the txv's opening position if the equalizing line is restricting the leaked refrigerants flow into the suction line.


    I've only seen two txv's fail in this way in 28 years so i know its not a common problem! I guess being stuck at home due to snow has got me wondering

  12. #12
    ariez238's Avatar
    ariez238 Guest

    Re: TXV/TEV equalizing line size?

    Actually I am still somewhat confused about the location of storage / expansion Bulb position either external or internal TXV, the distance between the TXV and Bulb Bulb also the position of those facing where? what influences of these errors Bulb position?
    Thanks

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. How to select the collect suction pipe line size ?
    By oilzee in forum Technical Discussions
    Replies: 4
    Last Post: 29-05-2010, 07:20 PM
  3. Dupont line size calculator also has 410a and 407c
    By 128cyclist in forum Tools and Calculators
    Replies: 6
    Last Post: 20-08-2009, 03:45 PM
  4. Suction line size too small
    By marc5180 in forum Air Conditioning
    Replies: 16
    Last Post: 11-08-2008, 05:41 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •