    Hello,
    My coleagues found a ***** leak in the liquid pipe cemented under a store. There is no access to the pipe. (we will eventually need to run another one to supply the evaporators)
    They used nitrogen pressure (24 bar) and it dropped to 20 bar in one hour.
    Is there any way to calculate aproximately the amount of ***** r404a lost over a day/month/year through such a leak? (last year we charged 400kg, this year we charged ~500 kg so far)
    The liquid pipe is aprox. 70 meters long in total by 54 cm in diameter.
    Feb 2009
    telford
    2,090
    33
    Re: how to estimate the amount of ***** leaking
    replace the pipe,cannot believe this question?who put it under concrete in the first place,did he wear a hat with bells on it.
    3,853
    Hi Nand,
    That sounds a pretty big leak, if its a liquid line it'll be even quicker to leak as it will come out as a liquid.
    Needs a new pipe run in as soon as possible, even if its just a temporary one till a neater proprer job can be made of it.
    In the UK we would not be allowed to recharge a system with a leak, not sure of the legal situation in Romania.
    Oct 2008
    mallorca, spain,
    75
    768
    why try to calculate a leak , replace the pipe pressure test , tripple evacuate gas up system , run on test, re- leak test, run on test , job finished,
    ireland
    1,450
    41
    i had this with a supermarket that shifted on its foundations, only affected the liquid lines tho. we replaced with stainless flexible hoses until the copper could be rerun.
    al
    nand's Avatar
    nand Guest
    Thanks, everybody
    Split Croatia
    57
    6,151
    36
    Quote Originally Posted by nand View Post
    With very complex mathematical functions I calculated your leak as:
    1,1 -1,36 kg/day
    33-40 kg/month
    400-500 kg/year
    Oct 2007
    Not Sure?
    I agree, Just change the piping. Change your oil and filters, New refrigerant and start over.
    Seriously! What was that guy thinking.
    Pentane rocks!
    nand's Avatar
    nand Guest
    1,1 -1,36 kg/day
    33-40 kg/month
    400-500 kg/year
    Braniac, i guess....
    400 kg/(last year =~ 12 months), 500 kg/(this year =~10 days at the time) that's an arithmetic i can't grasp.
    I was asking about calculating with refrigerant diagrams. You can't compute something and verify by computing it again, when you verify you must compute in another way and get to the same result.
    We found the leak, the liquid line was pressed on a water pipe.
  1. Why should you use new ***** after a repair
    By mastercheif602 in forum Fundamentals
    Last Post: 09-09-2009, 10:35 PM
  2. Dupont line size calculator also has 410a and 407c
    By 128cyclist in forum Tools and Calculators
    Last Post: 20-08-2009, 03:45 PM
  3. Water in *****
    By chemi-cool in forum Refrigerants
    Last Post: 17-08-2009, 10:16 PM
  4. How to control ***** charging amount
    By jyunp in forum Air Conditioning
    Last Post: 23-10-2008, 06:42 PM
  5. ***** and memory lapse
    By Tycho in forum Fundamentals
    Last Post: 30-01-2007, 11:17 PM