    Problem with Toshiba Ras 13 SKVR Dai Sei Kai



    I have mounted this air condition and owners said it's not working like in the begining . I take the test and it show me no error I send it to Toshiba they also said it ok. When outdoor is 5 deggress indoor unit can't worm over 23 . It's room about 20m2, 2,30m high .



  2. #2
    Join Date
    Mar 2008
    Location
    England
    Age
    68
    Posts
    250
    Rep Power
    17

    Re: Problem with Toshiba Ras 13 SKVR Dai Sei Kai

    I think you need to provide some more info e.g. what's the on / off coil temps (indoor & outdoor unit), fan speed and if possible pressure readings.
    I assume it's running on R410a?
    This looks like a nominal 4kW Heating system (at 20c room +7c outdoor).
    What's the heat loss / load for the room?
    On paper it should have more than enough capacity. Why do you want to heat room higher than 23c?
    If in doubt read the instructions. If still in doubt follow them.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Problem with Toshiba Ras 13 SKVR Dai Sei Kai

    You should run it in test mode and measure and record indoor heat exchanger air in and out temperature (when fan is high) and outdoor air temperature, and unit works more than 10 min.
    To activate test mode, press and hold RESET button for10 sec. (There will be one short beep.)

    According to that, and catalog data of air flow ( if fan is OK and unit and filters are clean) it could be calculated what is real emitted power of that unit.
    So, post your air temperature measurement here.

    Test condition for heating:
    Indoor 20°C
    Outdoor DB/WB 7/6°C
    Compressor speed 66 Hz
    Indoor fan high
    Outdoor fan high

    It should be measured:
    Pressure 26-28 Bar
    Pipe temperature at exit of indoor heat exchanger 41-43°C
    Pipe temperature at exit of outdoor heat exchanger 0-2°C
    Last edited by nike123; 09-01-2010 at 12:40 AM.

Similar Threads

  1. Toshiba VRF fan control board problem
    By multisync in forum Air Conditioning
    Replies: 2
    Last Post: 02-11-2009, 10:17 PM
  2. Toshiba RAS 13 SKV problem....
    By igi in forum Air Conditioning
    Replies: 17
    Last Post: 12-01-2009, 08:03 AM
  3. Toshiba ups problem
    By monkey spanners in forum Air Conditioning
    Replies: 0
    Last Post: 11-07-2008, 05:43 PM
  4. Toshiba RAV SM/SP1400 defrost problem
    By SteinarN in forum Heat Pumps
    Replies: 11
    Last Post: 20-02-2008, 04:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •