    Question York YDAJ gsi reciprocating chillers



    York YDAJ gsi chiller display system hanged. no any button functioning, and cannot getting any information.(chiller is working properly)
    Display board replaced and checked, but the situation is still the same. Pl give a solution.



  2. #2
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Thumbs up Re: York YDAJ gsi reciprocating chillers

    Quote Originally Posted by vinod View Post
    York YDAJ gsi chiller display system hanged. no any button functioning, and cannot getting any information.(chiller is working properly)
    Display board replaced and checked, but the situation is still the same. Pl give a solution.
    check ribbon cable which connecting display board to processor board.replace that.

    expecting your response

    Moideen-dubai

  3. #3
    Join Date
    Dec 2005
    Location
    uae
    Posts
    54
    Rep Power
    19

    Re: York YDAJ gsi reciprocating chillers

    Ribbon and display board replaced. but still the same situation

  4. #4
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: York YDAJ gsi reciprocating chillers

    it might be the trouble of Power supply board.check the voltage from power supply board J3 terminal,it should be 12VDC healthy.and also check the J1,J6 terminal from processor board,wire loose or misplaced.

    Moideen-Dubai

  5. #5
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: York YDAJ gsi reciprocating chillers

    i think there should also be a 5vdc test point on the board, check this also. This problem can(although rare) be caused by a faulty transducer or sensor.

    al

  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: York YDAJ gsi reciprocating chillers

    To add to the above excellent advise!
    Check if the control panel emergency stop device. Or any remote emergency stop devices are off?
    Last edited by Grizzly; 10-01-2010 at 07:45 AM.

  7. #7
    Join Date
    Dec 2005
    Location
    uae
    Posts
    54
    Rep Power
    19

    Re: York YDAJ gsi reciprocating chillers

    The problem solved by replace the key pad. Thanks to all.

Similar Threads

  1. York Chillers
    By N.Lewis in forum Air Conditioning
    Replies: 5
    Last Post: 17-11-2010, 07:36 PM
  2. centrifugal chillers york
    By Magic in forum Technical Discussions
    Replies: 6
    Last Post: 12-11-2009, 06:08 PM
  3. York & Trane Reciprocating Chiller
    By Gigas in forum Air Conditioning
    Replies: 3
    Last Post: 21-05-2008, 12:21 AM
  4. York Millennium Chillers
    By shairgr in forum Industrial
    Replies: 0
    Last Post: 10-12-2007, 03:04 PM
  5. York Reciprocating Compressor
    By lldelfin67 in forum Industrial Compressors
    Replies: 0
    Last Post: 17-07-2007, 03:56 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •