York YDAJ gsi reciprocating chillers
York YDAJ gsi chiller display system hanged. no any button functioning, and cannot getting any information.(chiller is working properly)
Display board replaced and checked, but the situation is still the same. Pl give a solution.
-
08-01-2010, 02:56 PM #2
-
09-01-2010, 03:10 AM #3
Re: York YDAJ gsi reciprocating chillers
Ribbon and display board replaced. but still the same situation
-
09-01-2010, 04:33 AM #4
Re: York YDAJ gsi reciprocating chillers
it might be the trouble of Power supply board.check the voltage from power supply board J3 terminal,it should be 12VDC healthy.and also check the J1,J6 terminal from processor board,wire loose or misplaced.
Moideen-Dubai
-
09-01-2010, 05:47 PM #5
Re: York YDAJ gsi reciprocating chillers
i think there should also be a 5vdc test point on the board, check this also. This problem can(although rare) be caused by a faulty transducer or sensor.
al
-
09-01-2010, 07:20 PM #6
Re: York YDAJ gsi reciprocating chillers
To add to the above excellent advise!
Check if the control panel emergency stop device. Or any remote emergency stop devices are off?Last edited by Grizzly; 10-01-2010 at 07:45 AM.
-
10-01-2010, 07:08 AM #7
Re: York YDAJ gsi reciprocating chillers
The problem solved by replace the key pad. Thanks to all.
Similar Threads
-
York Chillers
By N.Lewis in forum Air ConditioningReplies: 5Last Post: 17-11-2010, 07:36 PM -
centrifugal chillers york
By Magic in forum Technical DiscussionsReplies: 6Last Post: 12-11-2009, 06:08 PM -
York & Trane Reciprocating Chiller
By Gigas in forum Air ConditioningReplies: 3Last Post: 21-05-2008, 12:21 AM -
York Millennium Chillers
By shairgr in forum IndustrialReplies: 0Last Post: 10-12-2007, 03:04 PM -
York Reciprocating Compressor
By lldelfin67 in forum Industrial CompressorsReplies: 0Last Post: 17-07-2007, 03:56 PM