    Hot gas by pass valve



    Hi guys,

    We`ve got small job on that needs a bit of info on a HGBP. It`s a Alco but has no info on it. The parts buyer has had no luck describing it to the equipment manufacturer, Alco, HRP, Climate Center etc.
    So, here`s my question: I know capacity selection is critical for a TEV but is it the same for a hot gas valve? as long as the inlet/outlet connections are identical I can`t see a problem. Therefore could we fit a valve with the same connections. After all as far as I`m aware its sole purpose is to regulate the evaporator pressure.

    Thanks in advance guys,
    Glenn



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Hot gas by pass valve

    Can you describe the job? What sort of unit it is?

    Is this a new unit? Old one?

    Why do you need to add HGBP?

    Maybe an EPR will do the job?

    Details Glenn......

    It might develop into a basic discussion: HGBP Vs. EPR.

    There was a discussion about it conducted by the one and only, Mad fridgy.

  3. #3
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: Hot gas by pass valve

    Thanks chemi-cool
    Sorry, I should have put more info.
    It`s off a small compressed air dryer ( the original valve was faulty). I`ve not seen it, only going by a conversation with my boss. The compressor is about the same size as a domestic fridge. The hgbp is needed to keep the evaporating temp as near as 2c as possible. There`s very little room to in the cabinet and as the dryer`s a cheapo unit we want to keep the price reasonable.
    Oh, and the dryer`s built into an air compressor cabinet so we can`t fit a new dryer assembly inside it with out major surgery.
    Hope this helps.

    Mind you I have seen some dryers with EPRs come to think of it, could be a solution if all else fails.

    Thanks,
    Glenn

  4. #4
    Join Date
    Jul 2009
    Location
    Brisbane
    Age
    67
    Posts
    79
    Rep Power
    15

    Re: Hot gas by pass valve

    If you have the compressor capacity, the refrigerant type, the minimum operating evap temp and the condensing temp with the minimum evap load, your loca wholesaler should be able to size the correct DB valve for you. The problem with EPR valves is that the compressor ca operate below its design envelope at low loads and may overheat and fail.

Similar Threads

  1. LEV does not open
    By Yuri B. in forum Air Conditioning
    Replies: 7
    Last Post: 19-07-2009, 02:37 PM
  2. Oversize Relief Valve
    By Dacosta in forum NH3
    Replies: 1
    Last Post: 05-09-2008, 11:35 AM
  3. Service Procedures For TK Scroll
    By absolute-zero in forum Transport
    Replies: 0
    Last Post: 03-02-2008, 07:42 PM
  4. Compressor valve test
    By RackMechanic in forum Air Conditioning
    Replies: 11
    Last Post: 03-02-2008, 05:57 PM
  5. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •