    Fundamental



    Hi!

    My client has a space 1700sft. i calculate the cooling of the of the space that is 250kw.if i use the air cool type,TRANE chiller then what should be the capacity of the chiller & how to determine chiller capacity from cooling load.Is there any particular rule to calculate the chiller capacity from cooling load.



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Fundamental

    Quote Originally Posted by shameem View Post
    Hi!

    My client has a space 1700sft. i calculate the cooling of the of the space that is 250kW. if i use the air cool type,TRANE chiller then what should be the capacity of the chiller & how to determine chiller capacity from cooling load.Is there any particular rule to calculate the chiller capacity from cooling load.
    If you have 250 kW heat load, then your chiller has to be 250 kW. But I doubt you can install for 250 kW evaporators/coils in a 1700 ft³ space.
    What about air circulation?
    Cooling, freezing, AC....???
    What type of chiller you need? One who can retract 250 kW heat.
    There is no rule, especially not for such a capacities
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    412
    Rep Power
    22

    Re: Fundamental

    Quote Originally Posted by shameem View Post
    Hi!

    My client has a space 1700sft. i calculate the cooling of the of the space that is 250kw.if i use the air cool type,TRANE chiller then what should be the capacity of the chiller & how to determine chiller capacity from cooling load.Is there any particular rule to calculate the chiller capacity from cooling load.
    Hi shameem, 250 kw means 71 ton (250/3.516).for 1700Sqft required 71 ton.wonderful, how did you calculate? Make it clear.

    Moideen-Dubai


  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Fundamental

    Quote Originally Posted by shameem View Post
    Hi!

    My client has a space 1700sft. i calculate the cooling of the of the space that is 250kw.
    It must be some pretty hot goods and pretty short cooling time for using such capacity above freezing temperature (if you plan using water/brine chiller as source) in that space.
    Could you elaborate how you came to that number?

  5. #5
    Join Date
    Feb 2009
    Location
    usa
    Age
    43
    Posts
    7
    Rep Power
    0

    Re: Fundamental

    better to use HAP tool

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Fundamental

    Quote Originally Posted by RonaldoDaLima View Post
    better to use HAP tool
    What is HAP tool?

Similar Threads

  1. Ashrae Fundamental Handbook
    By NCN in forum Refrigeration Books
    Replies: 40
    Last Post: 28-01-2010, 11:49 AM
  2. Fundamental information
    By US Iceman in forum Fundamentals
    Replies: 12
    Last Post: 24-01-2010, 06:25 PM
  3. Fundamental question (air in the NH3-system)
    By NH3-Coolman in forum NH3
    Replies: 22
    Last Post: 25-09-2007, 10:46 AM
  4. The Fundamental Myth
    By Gary in forum Fundamentals
    Replies: 22
    Last Post: 18-09-2003, 12:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •