07-01-2010, 02:56 PM #1
Fundamental
Hi!
My client has a space 1700sft. i calculate the cooling of the of the space that is 250kw.if i use the air cool type,TRANE chiller then what should be the capacity of the chiller & how to determine chiller capacity from cooling load.Is there any particular rule to calculate the chiller capacity from cooling load.
-
08-01-2010, 10:48 PM #2
Re: Fundamental
If you have 250 kW heat load, then your chiller has to be 250 kW. But I doubt you can install for 250 kW evaporators/coils in a 1700 ft³ space.
What about air circulation?
Cooling, freezing, AC....???
What type of chiller you need? One who can retract 250 kW heat.
There is no rule, especially not for such a capacitiesIt's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
09-01-2010, 05:14 AM #3
-
09-01-2010, 10:49 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
24-01-2010, 02:54 PM #5
Re: Fundamental
better to use HAP tool
-
24-01-2010, 04:25 PM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Similar Threads
-
Ashrae Fundamental Handbook
By NCN in forum Refrigeration BooksReplies: 40Last Post: 28-01-2010, 11:49 AM -
Fundamental information
By US Iceman in forum FundamentalsReplies: 12Last Post: 24-01-2010, 06:25 PM -
Fundamental question (air in the NH3-system)
By NH3-Coolman in forum NH3Replies: 22Last Post: 25-09-2007, 10:46 AM -
The Fundamental Myth
By Gary in forum FundamentalsReplies: 22Last Post: 18-09-2003, 12:03 PM