    Fujitsu problems



    Hey guys,

    First timer to the site but im needing some help. I have a fujitsu ast9lsacw and i went to turn it on this morning and it wasnt producing any colder air after a minute or 2, i looked at the wall unit and the power light ( red ) is flashing 5 times, and the timer light ( green ) is continously flashing. Ive tried finding error codes, and even found one booklet from fujitsu but it doesn't give me flashes it just corrospondes in letters. I am still able to operate the unit, but it just seem's reguardles of the change in temperature on the handset it just keeps giving out room temp air. Any help would be much appriecated.

    Cheers daz



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Fujitsu problems

    Turn the unit off then on again. After that press test button on remote control (rear side) and look how many times now operation and timer LED flashes. Note that. Then press MANUAL/AUTO button on indoor unit until you hear 3 beeps from buzzer. That will erase error memory.
    Switch off and than on unit and see if indication repeat or it is gone. If it is gone, keep using your unit.
    If it is repeated post your notes here.

  3. #3
    Join Date
    Feb 2005
    Location
    Australia
    Posts
    123
    Rep Power
    21

    Re: Fujitsu problems

    hey Nike I should call you Quickdraw McGraw
    5 x Operation flash and a constant Timer flash indicates an outdoor unit control error. With this code flashing on the indoor unit, you need to point the remote at the unit and push the test run button. The flash pattern will change to a continuously flashing Operation light and a number of flashes of the timer light which gives more detail on what the error is.

    To get the unit to try to restart you need to push and hold the manual/auto button on the indoor unit for a few seconds then reset the mains power supply but leave it off for a minute or so for the unit to power down completely. If you are going to try this make sure you make a note of any error codes first if you have to get someone out to look at it, it will help them a lot.

  4. #4
    Oz_sparky's Avatar
    Oz_sparky Guest

    Re: Fujitsu problems

    hey airman, i tried as you suggested and now instead of the 5 operation lights and constant timer, it has reversed itself and is giving me a constant operational and 5 timer flashes per interval. Any ideas as to what the problem could be? Cheers for the info, any much would be much appreicated.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Fujitsu problems

    Compressor Location Error

    The compressor speed does not synchronize with the control signal. (Including start up failure of the compressor)
    > Permanent stop.
    [Diagnosis Point]
    - Check if 2 way valve or 3 way valve is left open.
    - Check the compressor (Winding resistance value, Loose lead wire).
    - Refrigeration cycle defective

  6. #6
    Join Date
    Feb 2005
    Location
    Australia
    Posts
    123
    Rep Power
    21

    Re: Fujitsu problems

    After the time delay when the outdoor unit is energised the condenser fan will start and you should hear some sort of noise from the compressor trying to start, does this happen?
    It is most likely to be a failed compressor especially if it makes unhappy sounds when it is trying to get going (ie sounds like it a car engine running on 3 cylinders or it is rattling or ticking) but it could also be the inverter drive. If you have access to a Daikin or EDC inverter checker box to hook up in place of the compressor then that is an easy way to confirm the inverter output is OK. The compressor winding resistances should be 0.512 ohms between each phases (it is a 3 phase compressor) unless you have a milliohm meter you will probably struggle to measure it to any real degree of accuracy. The tolerance is a maximum 5% imbalance ie 0.025 ohms!

  7. #7
    Join Date
    Jan 2010
    Location
    Bulgaria
    Posts
    7
    Rep Power
    0

    Re: Fujitsu problems

    Quote Originally Posted by nike123 View Post
    Compressor Location Error

    The compressor speed does not synchronize with the control signal. (Including start up failure of the compressor)
    Sometimes the error is produced by freezing of the compressors' oil. In our location we have 3-4 similar problems. After heating the compressor with external hot air gun for a 5-10 minutes, fix the problem.

  8. #8
    dhan's Avatar
    dhan Guest

    Re: Fujitsu problems

    can you please send to me the method statement of the installation of air handling unit(AHU)? Thank you

Similar Threads

  1. your opinons on fujitsu please
    By acgibo in forum Air Conditioning
    Replies: 18
    Last Post: 26-08-2009, 05:06 PM
  2. fujitsu three way valve problems?
    By capthummel in forum Air Conditioning
    Replies: 23
    Last Post: 06-05-2009, 09:17 AM
  3. Fujitsu or not?
    By LRAC in forum Air Conditioning
    Replies: 14
    Last Post: 29-08-2007, 09:45 AM
  4. Oil return problems
    By Peter_1 in forum Industrial
    Replies: 37
    Last Post: 23-08-2004, 11:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •