    Compute the first ammonia charge



    Hi everyboby:

    I have a NH3 liquid overfeed system and i don't sure how can i compute the ammonia charge? the system has the following components:

    • Low pressure receiver @ -42ºC
    • Low pressure receiver @ -37ºC
    • Suction line accumulator @ -5ºC
    • High pressure receiver
    • Evaporators
    • Condensers

    I need to know the basic rules for compute the ammonia charge.

    I hope that someone can help me.

    Best Regards

    Luis.



  2. #2
    Join Date
    Jan 2010
    Location
    USA
    Posts
    41
    Rep Power
    0

    Re: Compute the first ammonia charge

    personal stuff sorry
    Last edited by jaysephus; 04-02-2010 at 05:46 PM. Reason: personal stuff sorry

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Compute the first ammonia charge

    Calculate the volume of each component or pipe for the phase (liquid or vapor). Volume X Density = Mass. Mass is mass, so if you do each temperature requirement and then add the totals together you should be very close.

    For the pressure vessels, vertical orientation will be the easiest. For horizontal, the easiest method is to assume the vessel is half full of liquid, which is usually the recirculators. Half full is how the maximum capacity is defined, so I think it's reasonable to use this for holdup volume.

    If you get into trying to calculate the incremental volumes of horizontal vessels you will make yourself crazy doing the trig!
    If all else fails, ask for help.


  4. #4
    Join Date
    Feb 2008
    Location
    Lima - Peru
    Age
    41
    Posts
    49
    Rep Power
    0

    Re: Compute the first ammonia charge

    So much thanks guys

    I'm thinking to do the following calculate:

    V total = V low presure tanks * 0.5 + Suction line acumulator *0.5+ High presurre vessel * 0.5 + V evaporators + V condensers + V liquid feed line + V wet return line*0.25 ( i don't sure of this if the flow rate is 4)


    Is it Ok ?

    Obviusly i' m going to consider the evaporating temperature and if the refrigerant is liquid or vapor for compute the mass.

    Luis.

  5. #5
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: Compute the first ammonia charge

    luissandoval
    Luis as US Iceman had pointed out you should compute in mass (kg,lb)
    hear some teorical aspect
    v=vf+X*vfg
    v= specific volumen of the mixture
    X=mg/mt (quality of mixture)
    vf= specific volume of liquid
    vg=specific volumen of gas
    vfg= vg-vf

    You should figure out in kg or lb
    So, the mass (kg) will be

    m= V(volumen)/ v (specific Volumen)
    Ejem
    if a tank is half full
    mg= Volumen of gas / specific volumen of gas =Vt/2*vg
    ml= Vlumen of Liquid/ specific volume of liquid =Vt/2*vl
    mt=Vt/2*(vg+vl)

    in any case you could look in the mollier chart (P-h) the x,vg and vl values
    hope it can help
    best regards
    GWAPA

  6. #6
    Join Date
    Jun 2007
    Location
    South Africa
    Posts
    80
    Rep Power
    17

    Re: Compute the first ammonia charge

    I concurr - calculate the volumes/mass on the components that make up the whole system.

  7. #7
    Join Date
    Feb 2008
    Location
    Lima - Peru
    Age
    41
    Posts
    49
    Rep Power
    0

    Re: Compute the first ammonia charge

    Ok guys tha's right maybe i'dont explain you very good i'm goint to compute in mass but my question is about levels in tanks i don't sure if the levels in each tank and wet suction line are good someone could tell me if is it ok??

    Luis.

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Compute the first ammonia charge

    For the tank liquid level you have to make an assumption where the liquid level will be during normal operation.

    For the wet suction line remember this: the volume of gas can be high, but the mass is low. For liquid, it is the opposite. The mass of liquid returning to the vessel will be small. If you look at normal overfeed rate (which is the recirculation rate - 1) calculate the amount of mass coming out of each evaporator for gas and liquid for a given evaporator capacity. Then for each evaporator operating at that temperature you can use a ratio per capacity and add it all up.
    If all else fails, ask for help.


Similar Threads

  1. Ammonia Refrigeration License
    By jaysephus in forum NH3
    Replies: 21
    Last Post: 03-03-2010, 04:13 AM
  2. split inverter unsure of proper charge spec.. how to charge?
    By cadillackid in forum Air Conditioning
    Replies: 4
    Last Post: 19-11-2009, 01:52 PM
  3. Replies: 21
    Last Post: 03-02-2008, 05:10 PM
  4. Subcooling vs charge graph?
    By Larry2 in forum Fundamentals
    Replies: 4
    Last Post: 01-12-2006, 07:40 PM
  5. Who's in charge?
    By chillin out in forum Chit Chat & Service Stories
    Replies: 1
    Last Post: 01-10-2006, 10:51 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •