05-01-2010, 05:08 PM #1
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Suction Pressure and the CCPR
What is compressor model#?
-
06-01-2010, 01:59 PM #2
Re: Suction Pressure and the CCPR
Hello,
Thanks for responding friend.
The Copeland compressor is 1.5 HP/R-134/
kala-016e-tac-001.
I have product lit and access to Copeland website
but do not find info to address max. suction pressure.
-
06-01-2010, 03:36 PM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Suction Pressure and the CCPR
I also cannot find any data for R134a application. But for R12 is stated that is for medium and high temperature application.
Since R134a is replacement for R12 in high temperature application I think that you don't need CCPR at all.
Monitor your discharge temperature and amperage draw for various working conditions and base your decision according to that.
I also could be very wrong!
-
07-01-2010, 09:34 AM #4
Re: Suction Pressure and the CCPR
Regardless of the model number of compressor, why not just note FLA and set CCPR to that when comp running? Never overload compressor then.