May i have information of what i can look for and do when converting a coldroom to a freezer.I will be using the coldroom coil and the same condensing unit. I`m think its possible because the coldroom can reach temps as below as -5 degerees.
05-01-2010, 09:16 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: converting coldroom to freezerroom
No it is not possible.
Coil for freezing temperatures need to have higher distance between fins.
Condensation unit compressor is probably not designed to work with low mass of refrigerant which is case with freezer temperatures.
Find someone who know what he is doing.
05-01-2010, 01:36 PM #3
this will not work as a freezer you will need to check wall thickness and install door/floor heaters ect,ect.
05-01-2010, 01:44 PM #4
Change the coldroom coil to a freezer coil - add a new compressor and new condenser.
05-01-2010, 09:21 PM #5
Guys, guys, guys...
Of course it will work, just not very well.
Give the chap a break and let him try, then he can come back and ask us why it doesn't work afterwards.
07-01-2010, 03:24 AM #6
Yes, i agree with coolhibby1875 & viking. It will work but not quite good. For optimum performance of freezer you have to check for the proper thickness of panel insulation for the design freezing temp? provision of door/floor heaters to prevent air leakage, needs to change freezer coil with proper distance between fins, ect..
07-01-2010, 07:58 AM #7
It will work somehow but not well.
1. Check if the compressor can work in low tenp evaporation.
2. you will need to install temp controller for a freezer.
3. Defrost?? Only electric heaters can be added at the bottom of the evaporator.
4. changes in the control wiring should be made.
5. Check if the construction is thick enough for a freezer, otherwise you might get condensation on the walls and door. [100 mm polyurethane is minimum wall thickness]
6. Bare in in mind that electric consumption will be higher.
Apart from that - Best of luck.
I wouldn't do it.
07-01-2010, 08:16 AM #8
Hi Nike, good information, is there any method to find out the evaporator categorization? If we face like this problem, how do we find out this is cold room evaporator and this is freezer evaporator. You mention compressor type. What is the deference of freezer compressor than HT, MT compressors? I mean that any displacement variation, winding, material quality etc.
Moideen-dubai
25-08-2010, 12:02 PM #9
Hie guys after taking most of the things into consideration the only thing i didn`t do was to change the blower coil.I only added defrost heaters ,changed expansion valve(TX to TEX) and orifice. So far i have achieved -16 degrees.
25-08-2010, 12:27 PM #10
Wait for summer.
28-09-2010, 07:17 PM #11
dear kpo,
u have not mention what temp u want?
regds,
Glass in coldroom
By Crypton in forum CommercialReplies: 20Last Post: 20-11-2009, 12:43 AM -
coldroom cleaning products
By Lancs Bomber in forum Legal-Business-MarketingReplies: 3Last Post: 06-09-2009, 07:42 PM -
new coldroom installation
By chilltech in forum FundamentalsReplies: 8Last Post: 23-07-2009, 05:38 PM -
faulty EPR on coldroom
By fazzamouse in forum Supermarket RefrigerationReplies: 24Last Post: 19-11-2008, 07:22 PM -
how to earn hot water from coldroom
By water in forum Supermarket RefrigerationReplies: 1Last Post: 05-11-2008, 09:30 AM