    Evacuating Ammonia piping after repair



    I will be valving off the high side of a large ammonia plant for the purpose of replacing some isolation valves at the evap condensers. I will recover everything from the discharge service valves to the inlet to the receiver, including the thermosyphon. If I recharge the ammonia as liquid, once above saturation, is purging at the top of the system an adequate way of ridding the system of most of the non condensables or is evacuation necessary. The pump would have to be substantial, based on the time frame available.



  2. #2
    Join Date
    Dec 2008
    Location
    usa
    Age
    83
    Posts
    34
    Rep Power
    0

    Re: Evacuating Ammonia piping after repair

    Yes, evacuation pump is the best procedure. If time is of essence, after reharging the section you have isolated, before startin ghte compressors, run the evap condenser fans and water pumps for about 15 minutes to condense as much of the ammonia gas to liquid as possible, then purge from the highest point you can in each condenser. You will get air, water vapor and ammonia gas in your purge gas but the per cent ammonia will be lessened by making the condensers as cold as possible. If ambient is below 32 F, [like where I live], just run the fans.

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Evacuating Ammonia piping after repair

    Hi Phil2.
    definitly evacuate if at all possible, if time restricts, evac and purge.
    Does system have an auto-purger to clean up non-condensibles, I have found auto-purgers the best thing since sliced bread for keeping systems clean and tidy

  4. #4
    Phil2's Avatar
    Phil2 Guest

    Re: Evacuating Ammonia piping after repair

    Thanks. Running the fans is a great idea. The outdoor temp will likely be in the 30s

  5. #5
    Phil2's Avatar
    Phil2 Guest

    Re: Evacuating Ammonia piping after repair

    Yes, I do have a multipoint auto purger.

Similar Threads

  1. Ammonia Piping material
    By kpapa in forum NH3
    Replies: 12
    Last Post: 30-08-2010, 08:03 PM
  2. ammonia refrigeration system
    By Lc_shi in forum Fundamentals
    Replies: 48
    Last Post: 25-06-2010, 10:03 AM
  3. ammonia suction piping risers
    By Volnei in forum NH3
    Replies: 53
    Last Post: 20-04-2009, 11:03 PM
  4. Ammonia piping pressure relief system
    By BaTom in forum Refrigerants
    Replies: 4
    Last Post: 08-03-2009, 05:20 PM
  5. Ammonia Piping Specification
    By Volnei in forum NH3
    Replies: 19
    Last Post: 07-11-2008, 12:42 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •