07-01-2010, 03:39 PM #1
Re: SullAir/Jordan Valve
Originally Posted by jaysephus
Originally Posted by jaysephus
Then if for some reason the oil cooling load on one compressor decreases there is more liquid available for the remaining compressors downstream. If the Jordan valve is stroked all the way open when that occurs it has to throttle back. If it can't do this fast enough a sufficient volume of liquid may get into the compressor causing the alarms.
The flash gas in the liquid line is also caused by changes in pipe elevation. When a high pressure liquid line is installed to run vertically upwards the change in elevation reduces the liquid pressure due to static head penalties. This can be compounded installing a liquid line that is too small in diameter. This causes an increase in friction loss due to flow.
So... it is necessary to insulate a properly sized high pressure liquid line.
If you ever hear someone saying a 3/4" liquid line is sufficient for any reason you should ask them: based on what? And see what their answer is.
There are reason for why things work. Unfortunately, these are also the same reasons why things don't work.If all else fails, ask for help.
Similar Threads
-
LEV does not open
By Yuri B. in forum Air ConditioningReplies: 7Last Post: 19-07-2009, 02:37 PM -
Motorized Ball valve versus Globe valve for modulating application
By Sridhar1312 in forum IndustrialReplies: 2Last Post: 06-02-2009, 07:35 PM -
Service Procedures For TK Scroll
By absolute-zero in forum TransportReplies: 0Last Post: 03-02-2008, 07:42 PM -
Benji
By benji in forum Trouble ShootingReplies: 29Last Post: 30-01-2008, 01:25 PM -
TEV with MOP: how to keep valve body temp above bulb temp?
By DaBit in forum FundamentalsReplies: 5Last Post: 16-10-2002, 12:38 AM