01-01-2010, 04:19 PM #1
why CIC system ?
happy new year to all of you.
I have a blast freezer 4H-15.2 Bitzer compressor without CIC system ,room temperature -35°C by using R22 refrigerant .
I realised the compressor oil become brown colour . Last oil changing was 1 year ago . some people said i need to install CIC system to prevent oil colour changing .
could any body guide me where to get the information or article about CIC system and VARICOOL system ? when i need to fix those system and why install head fan ?
I have tried on GOOGLE search but still can not get what i want .
Your help would be much appreciated .
Regards
oilzee
-
01-01-2010, 05:01 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: why CIC system ?
Last edited by nike123; 01-01-2010 at 05:24 PM.
-
01-01-2010, 05:07 PM #3
Re: why CIC system ?
Hello Nike 123 ,thanks for your help .i 'm down loading the file .
-
01-01-2010, 05:33 PM #4
Re: why CIC system ?
let's say the system is using R507 refrigerant , Do we need to fix CIC system ?
-
01-01-2010, 05:41 PM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
01-01-2010, 05:51 PM #6
-
01-01-2010, 05:55 PM #7
Re: why CIC system ?
one more question.if i use it as a freezer storage ,room temperature from -35°C set it to -20°C , what would it be ? still need CIC system ?
Last edited by oilzee; 01-01-2010 at 06:04 PM.
-
01-01-2010, 06:27 PM #8
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: why CIC system ?
Varicool or CIC depend on size of compressor!
For R22 and room temperature -20 evaporation will be around -28°C and that require CIC or Varicool as well as aditional head cooling.
You cannot use capacity control when you have CIC !
http://www.bitzer.de/download/downlo...5.pdf&ccode=DE
Similar Threads
-
Daikin fault codes
By Chris2005 in forum Air ConditioningReplies: 45Last Post: 21-03-2012, 10:09 PM -
Ammonia Heat Pumps
By US Iceman in forum New TechnologiesReplies: 39Last Post: 22-03-2010, 06:36 PM -
Enthalpy Increasing Buffer System
By Reflexive in forum Technical SpeculationsReplies: 3Last Post: 23-12-2008, 03:18 PM -
Fan model for system optimization
By autt in forum System OptimizationReplies: 8Last Post: 31-03-2007, 05:34 AM -
Refrigeration system proposal; comments please.
By DaBit in forum Technical SpeculationsReplies: 13Last Post: 01-01-2003, 03:42 PM