    Over the years have noticed Vilter cylinder liners on 440 , 450's with 4 guide pins , have sealing problem on liner / discharge valve seat .
    The liners have very thin seat which discharge valve seats on .
    When discharge valve guide roll pins are inserted in liners the seat is damaged nearly everytime .
    Have pulled brand new machines apart and found poor sealing on these "lapped" faces .
    I usually grind side of roll pin and knock it in with ground side facing valve seat to avoid roll pin damaging seat .
    Its hard to believe that someone has not bought this to Vilters attention as it makes machine inneficient .
    Liners etc have to be removed to correct this seat and modify roll pins .
    Has anyone observed this fault and is is still a problem in new compressors out of the factory ?
    Jul 2006
    74
    865
    26
    Re: Vilter cylinder liner discharge valve seats
    I have looked at this before, but never had a problem with damaged seats. I am careful installing them and they seal up just fine.
    I will admit to being partial to Mycom however, as you get to lap the valve in and they seal well.
    3,355
    I worked on 2 x 442 which were relocated from plant in USA .
    Both were near new and on inspection found both had this problem where there was slight raised area where pins were installed .
    I figure they are all the same .
    Many years ago an Ausralian company made them under licence , but they never had guide pins .
    There was another offshoot of Vilter ith a few minor differences , probably for patent reasons . They were called Budge and had 2 sidecovers which helped a lot for assy but they used studs instead of bolts on sidecovers and heads so they were also APITA .
    Casting of machine guided discharge valve assy in place , seems much simpler to me .
    Mycom are good to work on and last few years we just get valve seats surface ground when possible .
  1. LEV does not open
    By Yuri B. in forum Air Conditioning
    Last Post: 19-07-2009, 02:37 PM
  2. Discharge Defrost Differential Valve
    By Phase Loss in forum Supermarket Refrigeration
    Last Post: 06-06-2009, 12:53 PM
  3. possible discharge valve fault symptoms?
    By sger9 in forum Trouble Shooting
    Last Post: 23-04-2009, 06:41 PM
  4. discharge valve
    By iceman3000 in forum Trouble Shooting
    Last Post: 23-06-2008, 09:25 PM
  5. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Last Post: 29-01-2008, 09:27 PM