Thread: oil cooling problem
-
14-03-2010, 05:58 AM #1
oil cooling problem
Dear All,
I started one screw compressor that is designed in condition -10 C as evaporating temp. and +35 as condensing temp. also this compressor is designed with fixed Vi
The pressure of liquid seperator (suction press) was 7 bar(a) in start.
The compressor worked at partial load (about 10% capacity) about 5min. after that high discharge temp. alarm turned up.
I think inner pressure of compessor at oil input of compressor has extra pressure rather discharge press. so oil circulation not been did correctly.
Please advise if you have idea
-
14-03-2010, 11:28 AM #2
Re: oil cooling problem
chichi ,
If compressor is differential oil feed it may cause this due to low oil flow, because little pressure difference between suction & discharge .
If lubricated and oil injection cooling by oil pump it should work fine .
Either load machine up or restrict suction valve on machine to achieve bigger pressure difference until plant settles down .
-
15-03-2010, 07:41 AM #3
Re: oil cooling problem
thanks a lot for your kind advice
-
15-03-2010, 07:42 AM #4
-
15-03-2010, 09:00 AM #5
Re: oil cooling problem
Hi, chichi
sometimes at very low partial load you can have a high oil temp .... RANGER1 gave you a good suggestion ... the best is to increase capacity a little to achieve more refrigerant to flow through compressor in your case suction gas had a very high temperature and flow was reduced - right way to get high oil temp ....(take care not to come to high discharge pressure)
Best regards, Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
Similar Threads
-
Liebherr fridge sounds, cooling and LCD problem
By bv1976 in forum Trouble ShootingReplies: 0Last Post: 03-03-2010, 11:31 AM -
Cooling problem with VRV REYQ24M7.
By cool#9 in forum Air ConditioningReplies: 3Last Post: 07-02-2010, 12:20 PM -
LG heat pump problem
By back2space in forum Heat PumpsReplies: 132Last Post: 01-02-2009, 11:23 PM -
Furance problem
By ALONEI in forum Trouble ShootingReplies: 10Last Post: 14-05-2008, 11:32 AM -
Regulation of cooling capacity
By npaisnel in forum DomesticReplies: 13Last Post: 08-02-2002, 11:22 PM