Results 1 to 8 of 8
Thread: Oil seperator?
30-12-2009, 03:33 PM #1
Oil seperator?
I have a copeland condensing unit which has ruptured a leak on the oil seperator, can this be bypassed temporarily? Or will it damage the system? The freezer is full of stock.
30-12-2009, 03:37 PM #2
Re: Oil seperator?
If the freezer is below the condensing unit, you might loose all the oil.
You did not mentioned the refrigerant in the system but increasing the superheat will help you bringing the oil back when you run without an oil separator.
30-12-2009, 04:01 PM #3
Re: Oil seperator?
Hi chemi, it has a 404 exp valve on it but it looks really old, it is above the evap, also the oil type is ester
30-12-2009, 04:28 PM #4
Re: Oil seperator?
If you cant get a new oil separator , recover the refrigerant and by pass it for a few days.
Look back in the forum for a post by nike123 about POE return. There is a different approach for the U oil trap.
You might have enough time before everything will defrost to make one.
On the other hand, nothing will defrost now in England
31-12-2009, 05:59 PM #5
Re: Oil seperator?
Thanks for that chemi, i bypassed it for now, will look at nikes post, you are right, nothing will defrost in england, im looking at 4 feet of snow outside my window haha.
31-12-2009, 06:45 PM #6
Re: Oil seperator?
Please come back after you have fixed it and tell us how did it go, some pictures will help us all to understand what was it all about.
03-01-2010, 01:41 PM #7
Re: Oil seperator?
Will do chemi!
06-01-2010, 08:33 AM #8
Re: Oil seperator?
"You did not mentioned the refrigerant in the system but increasing the superheat will help you bringing the oil back when you run without an oil separator."
why increasing the superheat will help bringing the oil back? I have never heard this kind of theory.
You mean: when the superheat increases, the expansion provide more refrigerant to the evaporator, and the oil will return to the compressor easily?
and when the superheat increases, the suction temperature increases too, so the discharge temperature increase too, and more refrigerant will leave the compressor with refrigerant.
diagnosing oil seperator problems
By paul pursehouse in forum Trouble ShootingReplies: 2Last Post: 29-12-2008, 10:22 PM -
oil seperator
By jakemag in forum Trouble ShootingReplies: 1Last Post: 19-10-2008, 04:01 PM -
Oil Seperator
By jwasir in forum FundamentalsReplies: 11Last Post: 19-09-2008, 02:24 PM -
oil seperator
By coolhibby1875 in forum CommercialReplies: 4Last Post: 31-10-2007, 03:06 AM -
Oil seperator trouble
By Comms1 in forum Supermarket RefrigerationReplies: 22Last Post: 29-11-2005, 09:42 PM