    Re: Pressure drop

    Quote Originally Posted by akcwby View Post
    I have a walk-in freezer with duel evaporators. There is approximately 90 feet of suction line back to the condensing unit. The suction line has solenoid valves, filter and an accumulator. Taking pressure reading at the compressor how do I find the pressure drop for superheat calculations?
    There's really no magic way. Installing an access fitting at the evap outlet is the only accurate procedure.

    Heatcraft's piping chart list the pressure drop for copper fittings and pipe.

    Here's the link to this manual. http://www.hvacrinfo.com/loadcalcs.htm

    Just curious, why is there a solenoid valve in the suction line?

    To find the pressure drop for the solenoid you will need to get the part number and brand of the valve and look in the manufacturers catalog. Same rule applies for the accumulator. Unless the suction filter has an outlet access fitting, it's a guess.
    Last edited by powell; 29-12-2009 at 09:23 PM.
    Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com

Similar Threads

  1. About liuid line pressure drop.
    By wilsoncheung in forum Technical Speculations
    Replies: 15
    Last Post: 16-03-2009, 11:34 AM
  2. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  3. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  4. TEV capacity related to pressure drop
    By DaBit in forum CPU Overclockers
    Replies: 8
    Last Post: 06-12-2002, 05:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •