    Question Pressure drop



    I have a walk-in freezer with duel evaporators. There is approximately 90 feet of suction line back to the condensing unit. The suction line has solenoid valves, filter and an accumulator. Taking pressure reading at the compressor how do I find the pressure drop for superheat calculations?



  2. #2
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Pressure drop

    Quote Originally Posted by akcwby View Post
    I have a walk-in freezer with duel evaporators. There is approximately 90 feet of suction line back to the condensing unit. The suction line has solenoid valves, filter and an accumulator. Taking pressure reading at the compressor how do I find the pressure drop for superheat calculations?
    There's really no magic way. Installing an access fitting at the evap outlet is the only accurate procedure.

    Heatcraft's piping chart list the pressure drop for copper fittings and pipe.

    Here's the link to this manual. http://www.hvacrinfo.com/loadcalcs.htm

    Just curious, why is there a solenoid valve in the suction line?

    To find the pressure drop for the solenoid you will need to get the part number and brand of the valve and look in the manufacturers catalog. Same rule applies for the accumulator. Unless the suction filter has an outlet access fitting, it's a guess.
    Last edited by powell; 29-12-2009 at 09:23 PM.
    Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com

  3. #3
    Join Date
    Dec 2009
    Location
    Alaska
    Posts
    5
    Rep Power
    0

    Re: Pressure drop

    Im sorry, there is no solenoid in the suction line. I planned on putting access fittings in next time it goes down. That is a great link thank you.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Pressure drop

    If you have an externally equalized TXV/TEV you may be able to put an access point at the valve balance line connector.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Pressure drop

    Pump down system and install a schrader access port at the point in system that the TX valve buld is fitted. Gauge at that point versus a gauge at compressor will tell all.
    Every bend ,fitting and pipe size and length of pipe will add superheat to compressor performance, and de-grade system performance accordingly. Try and keep max loses or super heating loses to max +5.0 ' C. Vertical head losses can be a killer with liquid lines loses producing flash gas liquid feeding TXV. System performance reduced.

    magoo

Similar Threads

  1. About liuid line pressure drop.
    By wilsoncheung in forum Technical Speculations
    Replies: 15
    Last Post: 16-03-2009, 11:34 AM
  2. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  3. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  4. TEV capacity related to pressure drop
    By DaBit in forum CPU Overclockers
    Replies: 8
    Last Post: 06-12-2002, 05:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •