    I have got a problem with a CVHG three stage centrifugal machine. On arrival this morning the machine was in fault, showing a phase loss fault, so checked it out. The start contactor pulls in for a second or so, drops out, pulls in again and drops out. The run or shorting contactors don't even pull in at all. I checked the mechanical interlock and that was OK, the CT's I decided to check, but thought I'd better look at the binding view first. I had 27 red faces. Nothing is bound. I tried to bind the components but nothing will bind. I can turn the LED's all on with a magnet, but when I try to bind the LED just goes out. I have the option on Techview to turn on and off all LED's, but it won't turn them on, so I had to use a magnet. For the individual components, the LED on and off options down the side is grayed out and not selectable, At first I thought it might have been the COM4 board, but now I think the controller may be faulty. I even unplugged the controller, plugged it back in and there's Comms Loss Motor Temperature 1, 2 and 3 faults which won't clear. IN addition there's a VCI Emmitter inside the control cabinet door, which has split (Although I don't actually think that's a factory fitted item)

    Has anyone else had a problem like this one???

    Thanks


    a problem shared is a problem halved

  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    55
    Rep Power
    16

    Re: Trane CVHG problem

    Hi, Does this unit have a 2 stage HP Switch? If so check that the second stage has not tripped.
    Also check all neutral connections are made.
    Good luck, and Happy New Year.

Similar Threads

  1. Trane CXAH/CGAH-240 problem
    By MortenOlsen in forum Trouble Shooting
    Replies: 7
    Last Post: 12-05-2010, 08:49 PM
  2. Problem with Trane RTAD100 chiller.
    By on4hf in forum Trouble Shooting
    Replies: 8
    Last Post: 14-10-2009, 09:01 PM
  3. Trane CCUH oil problem
    By wingman in forum Air Conditioning
    Replies: 25
    Last Post: 04-08-2009, 07:07 AM
  4. Trane Screw Chiller ECVA 275 Compressor problem
    By pkumar68 in forum Commercial
    Replies: 3
    Last Post: 31-12-2008, 09:20 PM
  5. Trane HP Defrost Board Problem
    By FastEd in forum Heat Pumps
    Replies: 8
    Last Post: 05-09-2008, 01:30 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •