Pump-down problems!
Hi everyone, new to this site and hope you can help me out. I have a problem with a maneurope compressor r404 which serves a walk in freezer.
Problem is when it pumps down, solenoid closes and compressor pumps down to around 8psi when LP switch knocks off unit, then pressure begins to rise quite fast to around 60 psi (suction) and unit cuts back in, and this process goes on and on. Would you say this was a solenoid problem or a compressor problem? What simple tests could i do to determine this? Thanks in advance.
-
28-12-2009, 09:14 PM #2
Re: Pump-down problems!
Hi Danny,
Could be either, fit your gauges on the suction and discharge valves on the compressor.
With the solenoid open shut the reciever valve and pump the unit down. After it has pumped all the liquid into the reciever does the pressure still keep rising?
If not, make sure solenoid is shut, and open reciever valve, if pressure now rises it looks like its a duff solenoid (you may see frost forming after it)
If the pressure keeps rising after the pumping down, it points to compressor problem, discharge check valve if its a scroll compressor (not familair with maneurop scrolls), oil seperator float/solenoid.
With the power off shut the dicharge valve, does this stop the pressure rising? if so thats how its getting in.
Basically you need to find out how the refrigerant is getting into the compressor, either through the suction due to duff solenoid, or through the discharge through duff discharge valves or external check valve if fitted, or possibly oil sepreator if fitted.
Jon
-
28-12-2009, 11:00 PM #3
Re: Pump-down problems!
Thats great jon, thanks for the advice, will check it 2moro, much appreciated!!
-
29-12-2009, 11:06 AM #4
Re: Pump-down problems!
if the room has a ball valve close that which elimanates the solenoid vavle but i would bet any money its the compressor i come across this all the time with maneuropes, it plays ahvoc with defrost as the contactor for heaters go through the aux on the comp contactor.
-
29-12-2009, 04:11 PM #5
Re: Pump-down problems!
what happens if you close suction valve,is the evaporator badly frozen?
-
29-12-2009, 06:46 PM #6
Re: Pump-down problems!
It turned out to be the compressor, thanks for the advice, could that affect the performance of the system? Defrosted the coil, system hits -10, sight glass just full, suction at 18psi, discharge at 175psi, once it hits -10 it starts frosting back on suction and struggles to get any colder, any ideas?
-
29-12-2009, 09:23 PM #7
Re: Pump-down problems!
have you replaced the compressor yet?
-
29-12-2009, 09:28 PM #8
Re: Pump-down problems!
no, but have ordered it for thursday, freezer is still full of stock and customer has nowhere to put it so need to get it another 5 degrees colder at least, if possible. Soon as it reaches -10 the coil and suction start to ice up quite bad, do u think the pressures seem about right?
-
29-12-2009, 09:48 PM #9
-
29-12-2009, 09:55 PM #10
Re: Pump-down problems!
air temp onto condensor is around 5 degrees, condensor is inside but has a hole cut in the wall, evap is completley clear, had electric heaters defrost it all, evap is single fan and is working correctly.
-
29-12-2009, 11:12 PM #11
Re: Pump-down problems!
I wonder whether you could improve the liquid flow by blocking the condenser to raise the pressure (just in the short term).
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
30-12-2009, 12:17 AM #12
Re: Pump-down problems!
Thanks brian, will give that a try!
-
30-12-2009, 01:23 AM #13
Re: Pump-down problems!
good call brian
Similar Threads
-
Liquid Pump Problems
By CanadianIce in forum NH3Replies: 13Last Post: 04-12-2009, 10:02 AM -
Heat Pump Problems South of Watford!!
By yinmorrison in forum Air ConditioningReplies: 7Last Post: 23-01-2009, 01:21 PM -
Water Pump Tripping Overload. (are you sitting comfortably)?
By Grizzly in forum ElectricalReplies: 14Last Post: 27-08-2008, 08:57 PM -
frostles heat pump
By Lc_shi in forum New TechnologiesReplies: 27Last Post: 31-03-2008, 07:53 AM -
Liquid Ammonia Pump problems
By smpsmp45 in forum NH3Replies: 7Last Post: 01-02-2008, 11:51 AM