    Pump-down problems!



    Hi everyone, new to this site and hope you can help me out. I have a problem with a maneurope compressor r404 which serves a walk in freezer.
    Problem is when it pumps down, solenoid closes and compressor pumps down to around 8psi when LP switch knocks off unit, then pressure begins to rise quite fast to around 60 psi (suction) and unit cuts back in, and this process goes on and on. Would you say this was a solenoid problem or a compressor problem? What simple tests could i do to determine this? Thanks in advance.



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Pump-down problems!

    Hi Danny,

    Could be either, fit your gauges on the suction and discharge valves on the compressor.
    With the solenoid open shut the reciever valve and pump the unit down. After it has pumped all the liquid into the reciever does the pressure still keep rising?

    If not, make sure solenoid is shut, and open reciever valve, if pressure now rises it looks like its a duff solenoid (you may see frost forming after it)

    If the pressure keeps rising after the pumping down, it points to compressor problem, discharge check valve if its a scroll compressor (not familair with maneurop scrolls), oil seperator float/solenoid.
    With the power off shut the dicharge valve, does this stop the pressure rising? if so thats how its getting in.

    Basically you need to find out how the refrigerant is getting into the compressor, either through the suction due to duff solenoid, or through the discharge through duff discharge valves or external check valve if fitted, or possibly oil sepreator if fitted.

    Jon

  3. #3
    Join Date
    Dec 2009
    Location
    UK
    Posts
    9
    Rep Power
    0

    Re: Pump-down problems!

    Thats great jon, thanks for the advice, will check it 2moro, much appreciated!!

  4. #4
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: Pump-down problems!

    if the room has a ball valve close that which elimanates the solenoid vavle but i would bet any money its the compressor i come across this all the time with maneuropes, it plays ahvoc with defrost as the contactor for heaters go through the aux on the comp contactor.

  5. #5
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: Pump-down problems!

    what happens if you close suction valve,is the evaporator badly frozen?

  6. #6
    Join Date
    Dec 2009
    Location
    UK
    Posts
    9
    Rep Power
    0

    Re: Pump-down problems!

    It turned out to be the compressor, thanks for the advice, could that affect the performance of the system? Defrosted the coil, system hits -10, sight glass just full, suction at 18psi, discharge at 175psi, once it hits -10 it starts frosting back on suction and struggles to get any colder, any ideas?

  7. #7
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: Pump-down problems!

    have you replaced the compressor yet?

  8. #8
    Join Date
    Dec 2009
    Location
    UK
    Posts
    9
    Rep Power
    0

    Re: Pump-down problems!

    no, but have ordered it for thursday, freezer is still full of stock and customer has nowhere to put it so need to get it another 5 degrees colder at least, if possible. Soon as it reaches -10 the coil and suction start to ice up quite bad, do u think the pressures seem about right?

  9. #9
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: Pump-down problems!

    Quote Originally Posted by dannyk View Post
    no, but have ordered it for thursday, freezer is still full of stock and customer has nowhere to put it so need to get it another 5 degrees colder at least, if possible. Soon as it reaches -10 the coil and suction start to ice up quite bad, do u think the pressures seem about right?
    what is the air temperature onto the condensor,are you sure the evaps clear and fans all running ,sometimes fans [paddle]in airflow of the other,is the water getting away [via drain]completely after defrost.

  10. #10
    Join Date
    Dec 2009
    Location
    UK
    Posts
    9
    Rep Power
    0

    Re: Pump-down problems!

    air temp onto condensor is around 5 degrees, condensor is inside but has a hole cut in the wall, evap is completley clear, had electric heaters defrost it all, evap is single fan and is working correctly.

  11. #11
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Pump-down problems!

    I wonder whether you could improve the liquid flow by blocking the condenser to raise the pressure (just in the short term).
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  12. #12
    Join Date
    Dec 2009
    Location
    UK
    Posts
    9
    Rep Power
    0

    Re: Pump-down problems!

    Thanks brian, will give that a try!

  13. #13
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: Pump-down problems!

    good call brian

Similar Threads

  1. Liquid Pump Problems
    By CanadianIce in forum NH3
    Replies: 13
    Last Post: 04-12-2009, 10:02 AM
  2. Heat Pump Problems South of Watford!!
    By yinmorrison in forum Air Conditioning
    Replies: 7
    Last Post: 23-01-2009, 01:21 PM
  3. Replies: 14
    Last Post: 27-08-2008, 08:57 PM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  5. Liquid Ammonia Pump problems
    By smpsmp45 in forum NH3
    Replies: 7
    Last Post: 01-02-2008, 11:51 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •